- Reaction score
- 45
I was also thinking of Reg 526.1 as well to why you should earth the back boxes with a lead.
I don't believe the screw achieves that ....
So your not confused, my position is;
I'm with putting the fly lead in, I think that is the right way. I am also on the opinion the back boxes is an exposed conductive part. regardless of it being buried in the wall.
But I am now starting think about it, but I have taken on board the thoughts and option of everyone on here and there information from and GN8. this is leave me with a question.
how would you code this on a EICR. C3 or not bother ?...
Anyway enough for today. Happy new year everyone we'll pick this up next year
I don't believe the screw achieves that ....
So your not confused, my position is;
I'm with putting the fly lead in, I think that is the right way. I am also on the opinion the back boxes is an exposed conductive part. regardless of it being buried in the wall.
But I am now starting think about it, but I have taken on board the thoughts and option of everyone on here and there information from and GN8. this is leave me with a question.
how would you code this on a EICR. C3 or not bother ?...
Anyway enough for today. Happy new year everyone we'll pick this up next year