medway spark

Hi guys
When periodically testing a property what depth do you test the system?
Is it the same as an install? tests all points (exceptions to ones that can be access) and does the test sequence have to be followed from GN3. Dead test then live tests.
Thank you
 
An EICR is inspected to a depth appropriate to the state of the installation and the results of the initial and following inspections as determined by the inspector.
The installation is tested to the described extent at 100%, less any general, discovered or specified limitations as identified in the extent and limitations section.
The test sequence from GN3 is a good guide to the testing procedure but the experienced electrician can see that an already energised installation may permit variances from the test sequence.
 
I start at around 40% of all points, if i start finding problems then begin digging deeper, if its all A1 im happy to leave it at that


I usually get a good feeling within the first few minutes of visually inspecting an installation as to the standard and condition
 

Reply to periodic inspection and test on domestic property? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Hi Guys, looking at doing Initial and Periodic inspecting and testing. Looking between the CandG and EAL Just wondering if I can ask peoples...
Replies
16
Views
648
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
446
Hello fellow sparks, I’m looking to do my testing and inspection course which starts on the 30th of April, but I have not got much testing...
Replies
0
Views
229
Solar PV preventative maintenance contracts. What do you guys like to include (and exclude) when putting together preventative maintenance...
Replies
0
Views
329

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock