Hi am doing my first periodic inspection for a restaurant, my understanding is that I need to test a percentage of installation, so can I test some circuits and leave others? And if I could perform a certain test on a circuit how can I fill the schedule of results? Thanks
Depending on the age and condition of the installation, it could be 100% of circuits need to be tested.
Paperwork from previous tests is a good place to start if they are available
The installation to be honest looks in a good condition, the problem is I could find any paper work from previous tests, and some circuits I can't power them off to do all tests, and now am confused how to fill the schedule of test results
percentage testing means testing a percentage of points on each circuit, but all circuits need to be tested. it does not allow for any circuits to not be tested at all.
I thought all circuits initially need fully testing no excuses
Then once you have done this you can agree to test a certain percentage of circuits at regular intervals
You can "not test" a circuit, for instance it is quite normal not to turn off a comms supply. However, use your initiative. In a restaurant its probable that there is little you cannot test, on the certificates there is a box which says operational limitations
We did an EICR a few years ago, everyone was happy we were turning power off and on etc, Monday morning, 2 network switches had blown their power supplies, just due to power off, power on,
Too many limits though and you end up with a piece of toilet paper.
You should have a really good reason for not powering down a circuit, just limiting circuits means you could be leaving potentially dangerous circuits in play.
Did you have to pay for the damage?
Have they never had a power cut? If so, it'd be interesting to find out the consequences.
Before carrying out the inspection, the inspector and the client or duty holder are to agree on an amount of the installation to be inspected. Depending on the installation you may find that only a small amount of the installation can be tested and inspected due to operational limitations and you may want to consider the frequency of inspections dependant on those limitations. There is no requirement only guidelines on percentages to be tested and inspected.
This is a restaurant not a global banking concern and with agreed early hours access there should bet no concerns.
yes you may be right but my reply was just concerning the actual requirement for percentages during an EICR
The thread in question is a restaurant so unless it is a 24/7 concern the actual testing would be 100% unless the client has confirmed otherwise.
Reply to Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, Carrying out a periodic inspection at a domestic installation. Semi- detached house on a row of houses. I cannot for the life of me...
Hi Guys, looking at doing Initial and Periodic inspecting and testing. Looking between the CandG and EAL Just wondering if I can ask peoples...
Solar PV preventative maintenance contracts. What do you guys like to include (and exclude) when putting together preventative maintenance...
Hi all, Probs a simple one here but when testing a 3 phase board for ze as part of a periodic inspection plus part initial verification of a...
Not really a Question but its more a Point that the other Education Bodies out there than City and Guilds Granted most Employment agency dont...