TONY JONES
would like you guys opinion on this scenario one of our guys carried out a periodic on a house for change of ownership and it appears that he failed to notice that a supply which unknowing to him was taken from a jb in the loft of a bungalow and through into the garage to other sockets and lights.
There was no indication of this on the consumer unit chart and he asked the occupier if there was any power to the garage and they said at the time NO POWER TO THE GARAGE.
i AM TRYING TO ASCERTAIN WHETHER OR NOT HE SHOULD HAVE PICKED THIS UP FROM HIS INSPECTION RECORDINGS R1+R2 FOR THE RING? AS WOULD THERE HAVE BEEN A HIGHER REDING AT ONE OF THE SOCKETS OR NOT? IF IT WAS SPURRED FROM A JB IN THE LOFT? i think he would have possible got a higher reading if he had done the r1 +r2 correctly on the ring cross over. Other than that he would have had no reason to actually go in the loft or would he?
YOUR THOUGHTS ON THIS GREATLY APPRECIATED
Cheers.
There was no indication of this on the consumer unit chart and he asked the occupier if there was any power to the garage and they said at the time NO POWER TO THE GARAGE.
i AM TRYING TO ASCERTAIN WHETHER OR NOT HE SHOULD HAVE PICKED THIS UP FROM HIS INSPECTION RECORDINGS R1+R2 FOR THE RING? AS WOULD THERE HAVE BEEN A HIGHER REDING AT ONE OF THE SOCKETS OR NOT? IF IT WAS SPURRED FROM A JB IN THE LOFT? i think he would have possible got a higher reading if he had done the r1 +r2 correctly on the ring cross over. Other than that he would have had no reason to actually go in the loft or would he?