I have a few questions about a periodic inspection and report given to me recently by a letting agent. the property was built in the early 1970's original Wylex BS3036 CU. Just wondered what you guys would code these items as:

1. no mains powered interconnected smoke detection to to comply with BS5839 part 6

2. redundant cable unterminated in CU

3. Black conductors at switches not sleeved as line conductors

4. no back plate to baton lamp holder in utility room

5. earth wires to utility sockets not sleeved

6. sockets mounted at less than 100mm from floor level

7. 16mm meter tails under sized for main fuse ( there is no rating or fuse type visible on the service head and the service head is sealed)

8. main earth 2.5mm under sized

I know that Periodics are a matter of opinion which is why I'm asking for you guys opinions. I have yet to take my 2391 so I consider this to be valuable experience.
 
I have a few questions about a periodic inspection and report given to me recently by a letting agent. the property was built in the early 1970's original Wylex BS3036 CU. Just wondered what you guys would code these items as:

1. no mains powered interconnected smoke detection to to comply with BS5839 part 6

2. redundant cable unterminated in CU

3. Black conductors at switches not sleeved as line conductors

4. no back plate to baton lamp holder in utility room

5. earth wires to utility sockets not sleeved

6. sockets mounted at less than 100mm from floor level

7. 16mm meter tails under sized for main fuse ( there is no rating or fuse type visible on the service head and the service head is sealed)

8. main earth 2.5mm under sized

I know that Periodics are a matter of opinion which is why I'm asking for you guys opinions. I have yet to take my 2391 so I consider this to be valuable experience.

1 I'd make mention of this with a N/A as a code-the report is to BS7671, not BS5839

2 Code 4

3 Code 4

4 Code 2

5 Code 4

6 Code 4

7 Code 2 if the fuse size can be seen

8 code 2
 
Can anyone explain why the main tails are undersized for the main fuse, if the main fuse size cannot be confirmed due to an unmarked and sealed service cutout? Does this also mean that the CU main switch is under-rated too, IIRC the Wylex BS 3036 bords had a main switch rating of 60A or 80A depending on no. of ways and therefore should this also be reported?
 
Is the box entitled 'supply device characteristics' filled in?

If not, you could maybe stretch the code for item 7 to a 3 (requires further investigation).

Has a figure for maximum demand been entered?
 
Is the box entitled 'supply device characteristics' filled in?

If not, you could maybe stretch the code for item 7 to a 3 (requires further investigation).

Has a figure for maximum demand been entered?

Bs1361 type 2 100A for "primary supply overcurrent protective device" ( I was taught that it you can't check the fuse put unknown and sealed in the box)

Also noted is main switch BS5419 isolator rated at 63A - should this be given a code 2?

The maximum demand box has been left empty!

The main earth has been recorded as 2.5mm, this is part of the DNO's incoming supply cable ( bare strands soldered to lead sheath), so the only rectification for this would be to get the DNO out to replace the cutout.
 
Last edited:
Well if the fuse actually is 100A then I'd stick with my initial code 2, even though 2 metres of 16mm would always be adequate 'in the real world'

The BS5419 switch is probably a 60A but really for me, this would involve an assessment of maximum demand before I applied any code to that.

Yes, where the DNO have previously supplied an earth connection, it is their responsibility to maintain it. Does this 2.5mm then go to a main earth terminal?
 
Yes, where the DNO have previously supplied an earth connection, it is their responsibility to maintain it. Does this 2.5mm then go to a main earth terminal?

Yes the 2.5mm is about 100mm long and goes to a MET. From this there is two green insulated cables (about 4mm2 each) going into the CU.
 
Last edited:
Was it supplied with a back plate, did the manufacturer intend it to be mounted on a back plate?

BS7671 makes particular mention of manufacturers requirements being adhered to even above and beyond the regulations.
 

Reply to Periodic testing questions. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
664
Hi, I have a couple of questions from the am2. The install bays have the cutout fuses in a adaptable box with just a banana plug on the earth...
Replies
0
Views
928
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K
I have just carried out an EICR. Earthing is TT. A 4mm green/yellow conductor leaves the CU and disappears under the conservatory, I get 158Ω...
Replies
20
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock