Discuss PFC Test Industrial RCD in the UK Electrical Forum area at ElectriciansForums.net
P
Pmarsh
Hi all, most of my work is industrial, I'm required to test a consumer unit in a hydro generation unit.
This is not an issue I'm just struggling with the PSCC Live test as there is an industrial RCD directly after the incoming supply from Scottish power due to us having to supply our own earth TT. I've managed a PEFC test on the board on the no trip setting of my megger MFT1552 and have Very low reading understandably due to the TT earthing arrangement.
Every time I try a PSCC test it trips the industrial RCD. Is there a way around this using my tester or will bypassing the RCD be the only option. I would like to do the test at the board as there's a 40meter 50mm supply cable running back to the supply metering room that I would like to take into account.
As I say most of my work is industrial, so not overly familiar with the tester.
Any help would be appreciated
Will your tester measure phase to phase? This shouldn't bother the RCD unit.
Rule of thumb would be to just double the PEFC but as it's TT and you're measuring low current it will likely be lower than it potentially could be.
Measure phase to phase as rob said.
I've got a megger mft 1552 and it's good for 500v so no bother there.
You could measure phase to neutral and double your reading as a rule of thumb but your pfc will always be the measured value between phases and if single phase on a TT phase to neutral.
What is an industrial RCD??
Yeah I've self named it as it's large takes 50mm cables and is used for the industrial work I'm doing.. imaginative I know ;), basically it's just a large 3 phase Schneider earth leakage MCCB as you stated rob. Ok will give phase to phase a go, thanks all.
How are you carrying out the PSCC test at the moment? It seems very odd that it should trip an earth leakage relay, have you tried adjusting the settings of the relay temporarily to allow the test to be carried out?
Reply to PFC Test Industrial RCD in the UK Electrical Forum area at ElectriciansForums.net
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...