Hi I know how to test PFC at the origin of the Installation but how do you test PFC at other points in the installation does this mean on the individual circuits like the ends of them, and what about the earthing conductor is it disconnected or connected.and if disconnected why?
 
Hi I know how to test PFC at the origin of the Installation but how do you test PFC at other points in the installation does this mean on the individual circuits like the ends of them, and what about the earthing conductor is it disconnected or connected.and if disconnected why?


Main earth and bonding should all be connected as you want the lowest loop impedances possible (that the parallel paths create) so that you get the highest posssible PFC and you can then select the correct short circuit capacity for the protective device.
 
You want to obtain the Maximum PFC possible so conduct the test at the origin with the earthing condutors and main protective onding condutors connected.

By carrying out at the origin this is the maximum value. Theres no need to conduct the PFC tests for each circuit as this is to determine the short circuit capacticity of the circuit breaker. If needed you can use the value recored at the origin to substitue values of the individual circuis. This is since the PFC will reduce due to the resistance of the circuits so using the PFC at origin will and save you time.
 

Reply to Pfc testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
787
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
790
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock