pfc
Discuss pfc in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
C
chrisjudd
hi, i am studying for 2391 i hope i am grasping most things but am rather confused over
where exactly to test for pscc and pefc i.e does one test at the cu only or at ceiling roses and socket outlets, i am new to this forum any help gratefully rxd
chris judd
PEFC & PSCC (or PFC) are the prospective fault currents under short circuit & earth fault conditions & should be tested at the cu, pscc = phase/neutral (double result for 3phase) & pefc = phase/neutral/earth.
You should also test at everyrelevent point of the installation, such as remote db's or basicaly where a protective device has to operate under fault conditions.
If you haven't got it, get a copy of Guidence Note 3 & you'll find all the info you need under section 2.7.15
Hope that helps
I think you test it at the farest ie ceiling rose/socket point of the circuit. don't quote me on the that. i'll get you an accurate answer very soon
You are on about Zs (earth fault loop impedance);)
Reply to pfc in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Hi everyone, I really hope someone will be able to help. So last night I tried to change 2 ceiling rose / pendant lights at my mother in laws...
Hello all, I'm replacing a 3-bulb spotlight with a standard BG ceiling rose but upon connecting, the light won't turn on; the problem is, I can't...
6K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...