can someone please explain why you multiply the answer by 2 on a 3 phase supply and do you record the highest or lowest reading and why. thanks
 
Your record the highest reading of either the PFC or PSCC current after multiplying by 2, although it is technically the square roof of 3. But the lowest of the Ze or Zdb values.

It is to allow for a as the name suggest a Prospective Short Circuit Current or Prospective Fault Current which could be between 2 phases rather than Live and either Neutral/Earth.
 
can someone please explain why you multiply the answer by 2 on a 3 phase supply and do you record the highest or lowest reading and why. thanks

I don't see 3 phase in the domestic that I do but I imagine you test all three phases and find the highest and then x2 because you have 2 other phases?

Hope I have that right otherwise I'll look a right prat lol

You record the highest reading between pscc and pefc
 
As Dillb has said. The rule of thumb is to double it but if calculations are getting tight try multiplying by Sqrt of 3 (1.723) which can give you a little leeway.
 
In addition to the other posters Which are correct, it is because not all testers are capable of measuring across phases (Phase to Phase).

So you measure each of the phases in turn to Neutral and then double the highest reading, which errs on the side of caution giving you the max PSSC reading.

Your PEFC reading is just each phase in turn to Earth, again you take the highest reading.

You then take the highest reading of either the PEFC or your now doubled PSSC reading, and record that as the PFC.
 
Following on from Dillb, when you take a measurement of PFC on a loop impedance tester, the instrument is simply utilising the loop test and then applying ohms law to display the result in Amperes instead.

So what is the difference with a test between two phases? Well the resistance of the loop under test is typically the same, however the voltage that would occur in a fault between two lines will be 400v instead of 230v. So instead of applying the 230v in the ohms law equation we should use 400v.

But as our tester was already using the 230v source we have to convert it from 230v to 400v. As Dillb stated, this is more accuratley done by multiplying the value by the square root of 3.

However, as the purpose of the fault current measurement is for verification of selected protective devices breaking capacities, simply doubling the measurement as a rule of thumb provides a slight over estimation - which results in 'over compliance' consideration.
 
Following on from Dillb, when you take a measurement of PFC on a loop impedance tester, the instrument is simply utilising the loop test and then applying ohms law to display the result in Amperes instead.

So what is the difference with a test between two phases? Well the resistance of the loop under test is typically the same, however the voltage that would occur in a fault between two lines will be 400v instead of 230v. So instead of applying the 230v in the ohms law equation we should use 400v.

But as our tester was already using the 230v source we have to convert it from 230v to 400v. As Dillb stated, this is more accuratley done by multiplying the value by the square root of 3.

However, as the purpose of the fault current measurement is for verification of selected protective devices breaking capacities, simply doubling the measurement as a rule of thumb provides a slight over estimation - which results in 'over compliance' consideration.

I wish i could explain it that well!

Cheers.......Howard
 

Reply to pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Assuming that you measure the windings for a power transformer, for example: A-B: 2,258 ohms B-C: 2,262 ohms A-C: 2,250 ohms, how do you...
Replies
1
Views
531
Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter)...
Replies
7
Views
1K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock