Came accross an install today where a new 2 way board has recently been installed to make room for a new shower circuit (Db1 - 16th edition full board).

How the 'electrician' had wired it was by using 16mm tails from DB1 main switch which now has 25mm and 16mm crammed in there (please note there are no cores cut). I no this is not the correct way but now the customer is asking which regulation this does not conform too (basically I don't think he trusts me).

The main service fuse was marked up as a 1361 type ll 60amp.

Can somebody please shine some light on this please, I don't think ill be reattending to split the tails with a henley block anytime soon :p

Thanks
 
I no this is not the correct way but now the customer is asking which regulation this does not conform too
tell the customer that the rules are has follows .
1) get the numbty to come back to put the tails in tail block.
2)over crowding the manufactures instalment of the isolator.
3) putting a strain on the isolator .
4) walk from the job and tell him you will not be back.
 
Last edited:
Could try and use 434.3.iv

Then advise that the DNO stipulates the tails installation be changed to meet thier requirements - may only apply to DNO tails but let's not split hairs, customer wants a reg number and you've now got one.1581781931798431727967.jpg
 
I'm not sure there is. More likely its what the manufactures instructions would say. I'm thinking of the internal fly leads for feeding RCD's, with the welded cable ends. You can put more than one cable in an mcb. Not that I would try & put two large diameter cables in one terminal.
 
It comes down to engineering judgment really doesn’t it.....you can run 2 radials or both legs rfc from an mcb but realistically you wouldn’t start adding more circuits for practically.....I can’t imagine that main switch with a 25 and 16 mm cable in it is clamped down to well?
 
If it's done with care I cant see a problem, the only regulation breached might be the requirement to take into account manufactures instructions, who will stipulate a maximum conductor size for the terminations.
However if the connections are tight, secure and how no signs of thermal damage then I feel it's bordering on 'Jobsworth' territory to insist it's changed. If the above applies I would just note it on the comments box of my cert.
[automerge]1581792620[/automerge]

4) walk from the job and tell him you will not be back.
If we all 'walked' every time there was a non compliance on an existing installation which a client was reluctant to spend money on nothing would get done.
Ridiculous post.
 
If we all 'walked' every time there was a non compliance on an existing installation which a client was reluctant to spend money on nothing would get done.
Ridiculous post
the op has pointed out to a customer that the 25+16=41 mm tails are put in a
isolator ,and there for the design are made for 25mm tails not 41 , you could get away with it many years ago, but not like the olds wylex isolators with a couple of screw to terminate the tails .
 
the op has pointed out to a customer that the 25+16=41 mm tails are put in a
isolator ,and there for the design are made for 25mm tails not 41 , you could get away with it many years ago, but not like the olds wylex isolators with a couple of screw to terminate the tails .
I didn't say it was compliant, but if the OP is carrying out other work and the customer does not want him to remedy this, he just needs to verify that the connection shows no sign of thermal damage, and is secure and tight.....and note exactly that on his cert.
Walking away because of a relatively minor deviation from the regulations which does not form part of the work being carried out is plain daft.
 
While I accept this sort of thing is not uncommon and even allowed in regs subject to having a fault protection capable of protecting the cable to the sub-main, the question would arise what is the main fuse? For 16mm tails let's hope it's not 100A! But then I imagine taking in to account manufacturers installation instructions most of us would baulk at doing this as we would not comply with said instructions, wouldn't we? I personally don't like putting different size cables in the same termination due to difficulties in securing a good termination.
 
@digital_boy You could refer to regulation 462.1.201 "A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation."
 
While I accept this sort of thing is not uncommon and even allowed in regs subject to having a fault protection capable of protecting the cable to the sub-main, the question would arise what is the main fuse? For 16mm tails let's hope it's not 100A!
The OP has stated that the 16mm tails serve a fixed load that will be under the current rating for the tails. A 100a fuse protecting a short section of tails is compliant. Overload protection can be omitted and fault protection will be adequate
 
I didn't say it was compliant, but if the OP is carrying out other work and the customer does not want him to remedy this, he just needs to verify that the connection shows no sign of thermal damage, and is secure and tight.....and note exactly that on his cert.
Walking away because of a relatively minor deviation from the regulations which does not form part of the work being carried out is plain daft.
If it leads to argument/disagreement/lack of trust you're better off walking away. You ridicule someone...for stating their view, without taking this into account. All situations are different but, in this one, it seems the OP is worried that there is a lack of trust.
 
If it leads to argument/disagreement/lack of trust you're better off walking away. You ridicule someone...for stating their view, without taking this into account. All situations are different but, in this one, it seems the OP is worried that there is a lack of trust.
True, but there is no need for this to result in an argument or disagreement. The customer has not unreasonably asked which regulation is breached, clearly with a desire to find out why the OP considers the necessity to rectify. My opinion is that the reasons can be explained to the client, but that if there is no evidence of thermal damage or reason to suppose there may be in the future, there is no need to come over all jobsworth and walk away. No need for arguments and disagreements. If the OP is engaged in other work he notes it on his cert and states that the client was informed and declined remedial work.
I'm not surprised there is a lack of trust when the OP has condemned something as requiring rectification but is unable to give a reason other than 'it's not right'.
Just saying.
 
I would go with manufacturers instructions should be taken in to account. Can't remember the reg number.
Then find a pdf of the relevant MI.
Although it's R.A.F. It's something I've seen a few times with no ill effects.
 
Can't remember the reg number.
Then find a pdf of the relevant MI.
Although it's R.A.F. It's something I've seen a few times with no ill effects.
Could try and use 434.3.iv

Then advise that the DNO stipulates the tails installation be changed to meet thier requirements - may only apply to DNO tails but let's not split hairs, customer wants a reg number and you've now got one.View attachment 55793

Give the DNO a call, advise them what you can see and ask if they permit consumer tails to installed that way, if they don't then there's your deviation/breach of reg 434.3.iv.....no?
 

Reply to 'Piggy backing' tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
877
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock