skiandy

Hi,

I have just been asked to do a PIR on some small industrial units where the PME supply is extended to units in outbuildings. The main installation was completed 20 years ago when there was a 11kv transformer. Since then the DNO changed the supply to PME. Some of the units have earth rods but they are not configured as TT Systems, because the supply form the meter room is in SWA terminated in metal distrubtion boards. Ze on all the distrubtion boards checks out ok for TN-C-S but my understanding is that the PME supply should not be extended to the out buildings. Any recomdations/ideas?

Andy
 
I'd say it's not a problem so long as the normal things are in place at the outbuildings such as equipotential bonding. you'll need to use the adibiatic to make sure the mec to outbuildings meets the csa requirements of 7671 though.
 
The outbuildings are suitable for PME as they are build from stone, there are no other services run in; no gas and water is in poly.

The CSA of the SWA is enough to support the PME bonding as well as the CPC. I just can't see the point of the earth rod being sunk. As it's a PIR I can't really justifiy the recommendation that the installation should be split up i.e. terminate the SWA in a plastic inclosure and then run tails to the distrubution board....
 
The outbuildings are suitable for PME as they are build from stone, there are no other services run in; no gas and water is in poly.

The CSA of the SWA is enough to support the PME bonding as well as the CPC. I just can't see the point of the earth rod being sunk. As it's a PIR I can't really justifiy the recommendation that the installation should be split up i.e. terminate the SWA in a plastic inclosure and then run tails to the distrubution board....

well using spikes with PME is quite acceptable, remember the ME bit is Multiple Earthing. The regs actually say ' an electrode may be required at or near the consumers installation' or words to that effect;)
 

Reply to PIR Industrial units, Extended PME. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Metal shed In Garden with no extraneous conductive parts House electrics PME supply Garo make a 40a PME fault detection unit for EVs and I was...
Replies
4
Views
2K
I am about to install 4 sockets in 4 separate stone enclosures, housed within a large stone outbuilding. They have stone floors and are completely...
Replies
7
Views
2K
Done this loads of times before, but this situation is quite unique so bare with me. I've been asked to cable up an out building at a country...
Replies
5
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock