My uncle wants his property tested as theres a new tennant going to be moving in and just by looking at it i can see its only his sockets that have rcd protection, shower etc don't. What code does this go down as on test sheet and do they have to be changed so that all circuits are rcd protected. I know they obviously need to be on new builds etc just not sure how it works relating to older builds that were up to the regs at the time. :)
 
Do your PIR. Make sure all circuits meet required disconnection times ( Zs Readings ) . I would code 3 or 4 it, personally, but see what others on here say
 
As long as disconnection times are met, then you can leave as it is and give it a code 4 "recommendation".
But make sure everything else is safe and installed correctly as you check the installation.
Best regards,
Sav
 
agree with sav but if it's a TT earthing arrangement, I would like to see RCD on everything
 
Cheers for replies. I'll see what the test results show up! Also came across a shower and sockets that was on a 100ma main rcd the other day. Wasn't a tt system either, should this be changed or is it also ok as long as it meets disconnection times also? The testing I've managed to get to grips with no bother, it's the paperwork! Dare say I'll get used to it the more I do though!
 

Reply to PIR Question in the Australia area at ElectriciansForums.net

Similar Threads

Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
782
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
278
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock