OSG says 2m max, but doesn't refer to regs and I've read 537 and nothing to be found. So:

Got a customer wants to fit a lovely big range cooker in between two windows, perfect fit and will look great. Nowhere for the isolator to go except on an adjacent wall, around 4m wall length / 3m diag from appliance.

Whats says we?
 
I says put it where you can.
The OSG is only a recommendation, if it doesn't refer to an actual reg(?)
Maybe note it as a deviation from the OSG

edit, too slow!
 
The 14th and 15th editions had Regulations for how far away a Cooker Control Unit should be from the cooker. 6' and 2m respectivly.
The 13th just said that a CCU may be used and should be readilly accessible, the 16th and the 17th have no specific Regulations for cookers.
 

Reply to placing cooker switches in the Australia area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
615
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
HI! I'm a disabled guy, Cerebral Palsy, Hydrocephalus, Dyspraxia and Asperger's, who's been put into (basically) a one-room flat, there is a...
Replies
5
Views
1K
Been having a debate with a mate this afternoon about a circuit in his house. The circuit is a radial with 16 amp mcb that was previously used to...
Replies
6
Views
19K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock