is this existing or new? if it's how you plan to install, then it's back to the drawing board. what's the earthing system?

- - - Updated - - -

if it's how you plan to install, then it's back to the drawing board. what's the earthing system?

- - - Updated - - -

start again
 
Its a replacement of existing one. CU is close to the meter, but only RCD and 100A isolator installed, then is going for first floor, to flat, where sub-CU installed. Its extreme small flat with very limited devices, 7 sockets and electric shower, small oven and hob. Will be 5 circuts. One lights (6A), one sockets closed circuit (20A), Kitchen appliance circuit (32A), shower (40A 6mm cable), Oven (40A 6mm cable) and 100A isolator switch. There is TNS-C.
 
so what is the job you are doing? is it the flat CU only? those 15m tails should have fuse/MCB protection.
 
protect the 16mm tails with a 63A MCB. alongside the RCD.
 
Is it a good idea to have a single up front RCD? 15m away from the CU. I don't, nor do I think its a good idea to ever have a single up front RCD.
 
Its a replacement of existing one. CU is close to the meter, but only RCD and 100A isolator installed, then is going for first floor, to flat, where sub-CU installed. Its extreme small flat with very limited devices, 7 sockets and electric shower, small oven and hob. Will be 5 circuts. One lights (6A), one sockets closed circuit (20A), Kitchen appliance circuit (32A), shower (40A 6mm cable), Oven (40A 6mm cable) and 100A isolator switch. There is TNS-C.

Reading this, ...you're a electrical trainee aren't you?? Do you think you're ready to undertake a full rewire, even if it is an extremely small flat??
 
Couple of thoughts:
Where is the MET?

Following on from Murdoch's point,
If the 15m run currently requires RCD protection, can you replace it with SWA and remove the up-front RCD, replacing it with RCDs or RCBOs in the flat CU?
 
Couple of thoughts:
Where is the MET?

Following on from Murdoch's point,
If the 15m run currently requires RCD protection, can you replace it with SWA and remove the up-front RCD, replacing it with RCDs or RCBOs in the flat CU?
I dont find anything disturbing about 16mm2 6181y tail. Please, correct me if I'm wrong...

@Handy - MET goes together with meter.
 
I dont find anything disturbing about 16mm2 6181y tail. Please, correct me if I'm wrong...

@Handy - MET goes together with meter.

All I'm saying is that if you remove the RCD protection at the supply end and provide it at the flat CU instead, you need to avoid running the cable buried less than 50mm in a wall or use SWA or other suitable protection. See 522.6.101 of the current regs.

Are you planning to run the main protective bonding directly to the MET?
 
The OP diagram shows a 100a isolator feering a 63 amp rcd., not rcbo
Therefor rcd can be provided with more current than it can safely handle.

Boydy
 
The OP diagram shows a 100a isolator feering a 63 amp rcd., not rcbo
Therefor rcd can be provided with more current than it can safely handle.

Boydy

Why has the rating of his isolator got anything to do with how much current the RCD will see ? (As already stated in previous post RCD should be RCBO) As long as an isolator has a higher rating than it's supplying protective device (whose rating is not shown) it is irrelevant. It could be a 1000a isolator but if it was being supplied by a 60a fuse it would be fine ( overbuilt yes but electrically safe)
in industrial installations especially bus bar set ups very often the OCPD for the bus bars is a much higher ration of the switch fuses they supply.
 
Last edited:
Why has the rating of his isolator got anything to do with how much current the RCD will see ? (As already stated in previous post RCD should be RCBO) As long as an isolator has a higher rating than it's supplying protective device (whose rating is not shown) it is irrelevant. It could be a 1000a isolator but if it was being supplied by a 60a fuse it would be fine ( overbuilt yes but electrically safe)
in industrial installations especially bus bar set ups very often the OCPD for the bus bars is a much higher ration of the switch fuses they supply.


Because it looks like the op has fell into the trap of thinking a 63a rcd will provide overcurrent protection, for his 16mm tails thereafter.


Boydy
 

Reply to Please, see diagram and slap me if I am wrong ;) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Dear Community, I am at the initial phase of my camper van conversion in China, in which I am planning to live and work together with my wife...
Replies
0
Views
815
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
622
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock