BGB (section 704) states that plug sockets on a construction site if over 16A must be commando type.
Thats the only mention of sockets I can find, can I assume that 1363 sockets can be used in a temporary office area (probably a porter-cabin) that is generally waterproof etc?

Thanks.
 
Anywhere where the construction is carried out they have to be commandos anywhere else 1363s are fine.
 
Last edited by a moderator:
It's for a D&V Project.

I only have the green book, and it's says it's not different to the red.

704.511.1 says all assemblies for the distribution of electricity shall be in accordance to BS EN 60439-4
A plug or socket-outlet greater than 16A shall be to BS EN 60309-2.

That's abbreviated, but you mean the second part where it says 'ABOVE 16A shall be to BS EN 60309-2' ?
 
Just re-read your post and possibly read it properly this time!

704.1.1 vii (green) says 'administrative locations are not covered by Parts 1-6 of the scope'. Which I must have missed when reading it originally. And is the reg which agrees's with trev1's answer.

Thanks very much :)
 
I've always read it simply as that anything below 16A will be on a standard 13A plug-top (if site complies by RCD etc), anything on 110v is a yellow commando anyway, and anything greater than 16A again will almost certainly be on a ceeform (commando) and have it's own means of isolation by design.

You don't need steel toes and hard hats in a site office, hence why the other 'construction' dangers don't exist either.
 

Reply to Plug socket type on construction site? in the Australia area at ElectriciansForums.net

Similar Threads

I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
PoE details: Input: AC 100v~240v- 50/60Hz 0.3A max Output: DC 24v 0.5A PoE injector is used to convert mains AC into DC and power IP devices such...
Replies
17
Views
2K
Hi all, need some opinions on the following please> Origin is a three phase 60A TN-C-S supply.it goes into a changeover switch (small PTO driven...
Replies
59
Views
6K
D
Went to do a small addition on a construction site last week. The installation was installed and certed by others 6 months ago and consists of 3...
Replies
17
Views
5K
Hi all complete noob here, please note I am not an electrician by any means and I use the phrase "commando plug/socket" to refer generally to the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock