Discuss PME and isolators in the UK Electrical Forum area at ElectriciansForums.net
P
Plonker 3
Who is responsible for fitting the above, I always thought a supplier could install both.
But just been speaking to EON on behalf of a customer and they say they can fit a isolator but it is up to to the DNO to install the PME. :dunce:
I have always understood it as the DNO is responsible for the supply cable, its earth, the service head and the fuse. The supplier for equipment after that in the chain, tails to meter, meter, isolator. Anything after that is the end users.
Well I was sent to a job where I found a gas leak and the letting agent asked me to stay and call out Transco who then had to get permission from the supplier as they may have wanted to use their own contractor so it got kicked around the doors until they got the nod.
Just to add they are not responsable for the earth plus if you look at the latest edition of switched on the Electrical Safety Council where "dissapointed" at the governments refusal to force suppliers of smart meters to fit an intergrated isolator apparently the DNOs managed to lobby the government that an isolator was not required yet my thinking is they should just fit a stand alone one whilst they fit a new meter or service head. It really annoys me the way they can just brush everybody off plus I got called out to a job where the just changed the service head and then told the owner the main earth was too small (6mm) then they said get an electrician and to make matters worse they refused to connect the 6mm into their MET:mad2:
I had one where they moved the supply and fitted a new meter, 100amp tncs, in external cupboard.
I was going off site for a short time when they asked if I had some 16mm g/y, none available. I said i'd be half an hour and pick some up. Then one shouted he'd found some in the van. When i got back I noticed they'd fitted 10mm, shot off and didn't even mention it, or leave a message.
I've only known Western Power to install PME here, and have been at jobs where supplier has had to call out Western Power for PME. But I have seen supplier install isolators before. Western Power love to fit the isolators as they have a huge mark up on them.
Dillb, I had exactly the same thing several weeks ago, and after many many calls to EON and UKPN, here was the outcome...
Firstly, Eon will connect you to a PME provided that the correct neutral block has been installed AND there is a PME sticker from the DNO in place.
The DNO will not connect you to PME because they say they are not allowed to (that is EON's job)
So, for me, it involved getting UKPN out, who installed the neutral block and checked the EFLI.
They then had to come out again to put a sticker on the board.
Once the sticker was in place EON were happy to come out and connect to the supply as a PME plus fit an isolator at the same time if you require one).
Hope this helps.
Reply to PME and isolators in the UK Electrical Forum area at ElectriciansForums.net
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
If there isn't a 2-pole isolator there already, I usually get the client to arrange to get one fitted before I do a board change, either through...
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...