Supply neutrals do fail and either go high resistance or open circuit.

I can't understand why everybody says its a rare occurrence since everybody I know says they have had PME problems. So its not as rare as some people make out.

Farms are your best bet for fireworks. I had one a few years ago where all the showers went live, the lights all blew and we had glowing 'stars' in the corrugated metal shed where the current was using the metalwork of the shed as a return earth path.

Now the IET, in one of their periodicals recommend that you should stake the pme supply at the MET. There is one small problem with this and that is everybody and his dog down stream of the fault will use your earth stake as part of their neutral return which could result in quite a few amps flowing through your green and yellow wires.
However, its wise to make sure your MPB is of a suitable size for the neutral and connected to the incoming services
 
But as we all know, the laws of physics changed when coincidentally it became a tad expensive using TNS, so it'll be fine to use the N as an earth path.
 
It would seem some countries use a RCD with a built in over voltage trip to protect the consumers equipment.



This vector diagram shows what happens with a floating neutral.

 
Last edited by a moderator:
You are far more likely (if ever) to come across a high resistance supply neutral fault than a completely broken neutral, and that's a fact like it or not... You can check all the IEC and ITE and anyone else's reports/studies you like. They will all say the same thing, ''the incidence/occurrence of neutral breaks in low voltage supply distribution systems is so low, as not to even deserve consideration''!!! That's not to say that you should not protect against such an occurrence....

I take with a large pinch of salt, those that state they have seen numerous instances of broken neutrals on PME systems, it just doesn't happen, fortunately!!! I have a recently retired friend (DNO regional manager) that has only known of 3 such instances since joining, as was then, Eastern Electricity through to the time of his retirement in 2011, approx 35 years in total!!!

One of the easiest and cost effective ways of mitigating such problems to some extent, is to have a local earth rod at ''Each'' and every PME/TNC-S supply head, as they do in many European countries. But not at a numbty 200 ohm level, that would be a complete and total waste of time!!

Can't see why the combined over voltage/RCD devices that's been mentioned in this thread can't also be utilised in the UK either, that sounds like a reasonably solid idea, one that should be actively promoted.....
 
I can't help suspecting that there is a conspiracy of denial going on here.
Every electrician known to me, who's been in the game for a while has come across at least one failed neutral, that's not to say that it was open circuit, but more high resistance. As soon as the resistance rises beyond a few ohms it will begin to cause problems and will get progressively worse unless it is recognised and dealt with pdq.
I would certainly agree that spiking the MET at every supply intake will alleviate certain problems but will also hide them as well
 
i cant see how it would be a problem if all of the neutrakl curent was trying to go down one electrodwe. the laws of a certain mr ohm would take care of that. Aint you supposed to size the cable to the rod by best case resistance anyway? So in tother words, itys very unlikely that you would have a sub 10 ohms electrode. so the current that would flow would be 2.3 ohms. a 10mm cable for example would take that indefinately.
thy problem comeswhen people have undersized the cable to the rod, and you get a low current, long duration fault.
 
i cant see how it would be a problem if all of the neutrakl curent was trying to go down one electrodwe. the laws of a certain mr ohm would take care of that. Aint you supposed to size the cable to the rod by best case resistance anyway? So in tother words, itys very unlikely that you would have a sub 10 ohms electrode. so the current that would flow would be 2.3 ohms. a 10mm cable for example would take that indefinately.
thy problem comeswhen people have undersized the cable to the rod, and you get a low current, long duration fault.

You on the :54::)


Its the touch voltage you need to consider.
 
I can't help suspecting that there is a conspiracy of denial going on here.
Every electrician known to me, who's been in the game for a while has come across at least one failed neutral, that's not to say that it was open circuit, but more high resistance. As soon as the resistance rises beyond a few ohms it will begin to cause problems and will get progressively worse unless it is recognised and dealt with pdq.
I would certainly agree that spiking the MET at every supply intake will alleviate certain problems but will also hide them as well

I think it more a case of PME never being fully accepted in the UK by the older electricians, having been brought up, as it were with TN-S and TT systems. A single incident somehow turns into multiple incidents, and many electricians are simply telling of someone else's experience as their own, ...it soon spirals out of all recognition then.... Not so in the vast majority of Europe where you rarely, if ever hear any scaremongery about PME/TNC-S installations, that and TT systems is all they have ever known...

If as you say, every electrician of any age, has had experience of a PME failure of any description, then there would by now be a public outcry. Yes it does happen, but no-where near to the extent that some would have us believe. All the DNO's are very aware of the potential dangers of their PEN conductors and connections and go to great lengths to ensure the integrity of these systems. You only have to ring a DNO with just a suspicion of a problem involving PME/TNC-S supply and they will be generally there within the hour...

The way i see it, the conspiracy is from those perpetuating the myths and scaremongery that surrounds UK PME distribution systems...
 
You on the :54::)


Its the touch voltage you need to consider.

Fair point about the touch voltage, but that is the point of CPC's and equipotential/supplementary bonding, so that even if the touch voltage is high, then there is no potential between any extraneous or eposed conductive parts.
in my inmd there is little difference between the physics of current flowing down a rod, or down a pipe to earth. Eitrher way, if the bonding cable is sized correctly, it shouldnt pose a danger to the end user of the installation.

No alcohol by the way, just rubbish at typing fluidly/accurately at the same time!
 
Fair point about the touch voltage, but that is the point of CPC's and equipotential/supplementary bonding, so that even if the touch voltage is high, then there is no potential between any extraneous or eposed conductive parts.
in my inmd there is little difference between the physics of current flowing down a rod, or down a pipe to earth. Eitrher way, if the bonding cable is sized correctly, it shouldnt pose a danger to the end user of the installation.

No alcohol by the way, just rubbish at typing fluidly/accurately at the same time!

Several problems,

1, voltages within the equipotential zone maybe quite high.
2, it's sometime's difficult to maintain that equipotential zone.
3, high voltage's may appear outside.

A low Ra will limit the touch voltage, 200 ohm's no good, more like 2 :)
 
i agree with the need for low Ra's. If the Ra is relativley high compared to the extraneous metalwork, then theres really no point in it at all
I also agree that its difficult to maintain the equipontential zone. how many DIYers do away with bonding, because they have no idea, or misunderstand its purpose.

so can we come to an agreement that an earth rod on TNC-S supplies is good, as long as it has an Ra thats better than Ze with bonding connected/main earth disconnected?
 
I take with a large pinch of salt, those that state they have seen numerous instances of broken neutrals on PME systems, it just doesn't happen, fortunately!!! I have a recently retired friend (DNO regional manager) that has only known of 3 such instances since joining, as was then, Eastern Electricity through to the time of his retirement in 2011, approx 35 years in total!!!

One of the easiest and cost effective ways of mitigating such problems to some extent, is to have a local earth rod at ''Each'' and every PME/TNC-S supply head, as they do in many European countries. But not at a numbty 200 ohm level, that would be a complete and total waste of time!

Strange that 25 of them years I would have been a sparks, and had meetings at rayleigh EEB main office. (sadly a meter changer for a year) And my father was a chair man Of the ECA and was well up there as to SAY!(knew everyone) and your friend only told you of 3 such incedences!! yep its been well covered :)

as for 200 ohms, I totally 100% agree with you there.
((was looking for a thumbs up but couldnt find it!))
 
Last edited by a moderator:
It would seem some countries use a RCD with a built in over voltage trip to protect the consumers equipment.



This vector diagram shows what happens with a floating neutral.


The Tx would be solid earthed, if the PEN was broke the star point is still maintained , under-voltage would be the way to go, although the only way to limit the diverted currents is with a low impedance.

So one of these

http://www.hager.com.sg/energy-distribution/protection-devices/permanent-over-under-voltage-auxiliary-mz209-mz21/4844.htm


And an electrode me thinks.
 
Just another note on PME, about 2 months ago i was doing a CU change, I upgraded the bonding to gas and water. but when i was testing the Ze i got 11 Ohms! (TNS) ok i should have checked before. So I get the client to phone the DNO (ive tryed before but they only wana speek to the bill payer) and I parrot talk him through the fault.
Im fitting an alarm system as well in the property at the time so was around for a while, so in an hour the DNO turn up and check the Ze and he says yep it was probelly like this from when they did the joint in the road, using wooden joint boxes.
Two options TT the house or get the occupier to apply for TNCS,the 3rd option from the chap who turned up was I PME the head and he would re seal if needed! I went with option 3 but re sealed it myself! There was no care of what the condition of the undrground joints were in. so to say...

Quote E54 (not sure how to do this so i copy and paste)
All the DNO's are very aware of the potential dangers of their PEN conductors and connections and go to great lengths to ensure the integrity of these systems. You only have to ring a DNO with just a suspicion of a problem involving PME/TNC-S supply and they will be generally there within the hour...

Crock of Sh it..

Oh yer they were there in an hour but had no intrest in the joints, just wanted me to sort it out!

PS I have no issues with PME if done correctly. And not taken to outside sources, Like hot tubs, (Shudders)
 
Last edited by a moderator:
<snip> It is not a simple matter to retrofit TN-C-S distribution systems with such a facility. This is true for
TN-C-S systems (such as those in South Africa) that do not require the installation of a foundation
earth at the service entrance. Unless every consumer each have their own service entrance
foundation earth facilities, in the event of a break in the PEN conductor, the load current of all
other consumers may find a return path through those foundation earth connections that happen
to be present.
An extreme example would be the case of only one consumer having a foundation earth. In such
a situation, all the load currents of all consumers connected to that distribution system would try
to flow through the single foundation earth present. The consequential overheating together with
the related possibilities of incendiary ignition will be obvious.

In Cape Town nearly all the domestic installations I've seen are TN-C-S and look like this.

PME & Broken neutral untitled1 - EletriciansForums.net

PME & Broken neutral 2 - EletriciansForums.net

Every house has at least one earth spike.

There's two very different tiers of electrical distribution though, in the informal areas they use a maypole type system supplying multiple dwellings overhead from a single pole. I'm not sure what earthing system this system uses.
 
so in an hour the DNO turn up and check the Ze and he says yep it was probelly like this from when they did the joint in the road, using wooden joint boxes.
Two options TT the house or get the occupier to apply for TNCS,the 3rd option from the chap who turned up was I PME the head and he would re seal if needed! I went with option 3 but re sealed it myself! There was no care of what the condition of the undrground joints were in. so to say...

I've never seen or heard of buried wooden cable joint boxes. In the early day's virtually all underground cable joints would have been heavy gage cast iron with plumed lead joints!!!

And if the DNO electrician came to any job i was involved with and spouted off that sort of crap, i'd have been on to his manager, asking a few pertinent questions. One of which, would have been allowing a jobbing electrician to undertake connection alterations to a service cut-out!!!
 
Last edited by a moderator:
I've never seen or heard of buried wooden cable joint boxes. In the early day's virtually all underground cable joints would have been heavy gage cast iron with plumed lead joints!!!

And if the DNO electrician came to any job i was involved with and spouted off that sort of crap, i'd have been on to his manager, asking a few pertinent questions. One of which, would have been allowing a jobbing electrician to undertake connection alterations to a service cut-out!!!

Well aparently they have to apply for PME with who ever they pay their bills too.
The option was to dig up the street! but in his words its probelly best to PME the head, but as the meter was supplyed by someone else, it needs to be applyed for by the occupier. he even volentered to return and reseal, so he wasnt dodging the job, took me like 2 minuits. And as ive mentioned I worked for Eastern Electricity so it wasnt a big deal.
Looking back I could have kicked up a fuss, Have you ever tryed talking to the DNO!!! I bet NOT,, theres only so much Barry Manalow you can take....
 

Reply to PME & Broken neutral in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock