Just finished an EICR on a big 7 bed property. The incoming supply is PME. They have got the incoming head located approx 30m away from the Consumer Units. There is a Henley block in the mains and a previous contractor has ran a split concentric to a solid link fuse and then done another PME link under the consumer units. Therefore no connection to MET supplied by DNO. Is this acceptable?

Same job also has 2 sub mains from Henley block supplying an outbuilding and a pool house...they have exported the PME and have no earth rods locally...C3 or C2?
 
Hi All

Just finished an EICR on a big 7 bed property. The incoming supply is PME. They have got the incoming head located approx 30m away from the Consumer Units. There is a Henley block in the mains and a previous contractor has ran a split concentric to a solid link fuse and then done another PME link under the consumer units. Therefore no connection to MET supplied by DNO. Is this acceptable?

Same job also has 2 sub mains from Henley block supplying an outbuilding and a pool house...they have exported the PME and have no earth rods locally...C3 or C2?
You do not export the PME you are extending the equipotential bonding zone , which is perfectly acceptable.
Any extraneous conductive parts in the outhouses will be required to be provided with protective bonding at a minimum of 10mm2 copper as per table 54.8.
 
Same job also has 2 sub mains from Henley block supplying an outbuilding and a pool house...they have exported the PME and have no earth rods
Another possibility is to include the garage within the installation in the main dwelling and provide main equipotential bonding, in accordance with Table 54H (PME conditions apply), in practice this would mean a
10mm2 main bonding conductor would be required to connect the water pipe in the garage with the Main Earthing Terminal in the dwelling.
 
Incoming head is PME...but after the meter there is a henly block. Split concentric terminated into Henley block runs to solid link fuse 30m away and the earth for consumer units taken from neutral in solid link fuse
Hi - Don't know if I've understood correctly, but this might be a combined neutral and earth after supplier's cutout and if so, is likely forbidden by Regulation 543.4.1
 
Incoming head is PME...but after the meter there is a henly block. Split concentric terminated into Henley block runs to solid link fuse 30m away and the earth for consumer units taken from neutral in solid link fuse

What have they done with the earth in the split concentric cable?

I've seen something similar done once before by the DNO where they ran a straight concentric through the property to a red link at a second CU location.
 
Another possibility is to include the garage within the installation in the main dwelling and provide main equipotential bonding, in accordance with Table 54H (PME conditions apply), in practice this would mean a
10mm2 main bonding conductor would be required to connect the water pipe in the garage with the Main Earthing Terminal in the dwelling.
. . . and what have you done with Buzz?
 

Reply to PME exported from mains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
491
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
641
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth...
Replies
3
Views
531
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock