Hi All
Just finished an EICR on a big 7 bed property. The incoming supply is PME. They have got the incoming head located approx 30m away from the Consumer Units. There is a Henley block in the mains and a previous contractor has ran a split concentric to a solid link fuse and then done another PME link under the consumer units. Therefore no connection to MET supplied by DNO. Is this acceptable?
Same job also has 2 sub mains from Henley block supplying an outbuilding and a pool house...they have exported the PME and have no earth rods locally...C3 or C2?
Just finished an EICR on a big 7 bed property. The incoming supply is PME. They have got the incoming head located approx 30m away from the Consumer Units. There is a Henley block in the mains and a previous contractor has ran a split concentric to a solid link fuse and then done another PME link under the consumer units. Therefore no connection to MET supplied by DNO. Is this acceptable?