You are not exporting pme at all, the zone is extended not exported which is neither here nore there if it’s all part of the same building complex.
The 0.05 max resistance from the Met to the protective bonding conductors is totally inaccurate and unfortunately is banded about within the industry as a requirement when in fact it’s not.
The 0.05 figure was an indication of measuring between pipe work to determine if the pipes were relatively connected together by a low resistance if the bonding/earthing clamps could not be seen and were ‘built in’.
It’s all covered in GN3 which points out they the 0.05 figure is not between the MET and the bonding conductors.
 
Last edited:
Main bonding should be installed for each installation.
The installation in each flat is a seperate electrical installation and should have its own main bonding.

I disagree and you are contradicting yourself in both posts.. you could segregate one flat to a eicr or eic if works were on going but the OP asks about the ryefield & flats.

No, the size of the bonding is based on the size of the DNO's combined neutral and earth conductor. Neutral current diverted via the bonding under fault conditions will depend on this, not on the size of the supply to each flat.

Ultimately for a job like this the DNO should be consulted.

As there is one DNO supply to the OP property then bonding would need only be carried out from ryefield, in this case 16mm.

Dont know what @cliffed is on about exporting pme :/!!!
 
yes this is true, i spoke with the NICEIC and they say use tabe 54.8 for the ryefield or consult DNO, then each flat cant have any less than 10mm secondary main bonds

You need to install in accordance with BS7671 AND read your DNO policy document such as I linked to in post 18 and comply with this.
This covers bonding requirements towards the end.

Locally my DNO supplies and installs the Ryefield boards because they have had so many instances of refusal to connect to customer installed installations because of non-conformity with their requirements. The NIC are not supplying the electricity, you need to conform with your suppliers requirements
 

Reply to PME supply block of flats in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock