Pond pump is still tripping RCD which means I loose all power to socket outlets upstairs downstairs and kitchen (with freezer in it).Why doesnt mcb trip instead and what could be causing RCD to trip.Any advice would really be appreciated.
 
The RCD will trip on earth leakage, the MCB will trip on overcurrent. The 2 devices are completely different and perform different tasks.

Your RCD is tripping due to earth leakage in the pump, probably water as Tel said.

The MCB will only trip if you overload for any length of time, or under short circuit conditions.

Cheers..........Howard
 
The fault isn't due to 'overload' its due to 'earth leakage'.

MCB's work on 'overload'.

RCD's work on 'earth leakage'.
 
Can you unplug or otherwise isolate the pump from the circuit?...if it still trips there is a fault on the wiring,if it doesn't the pump is naffed. You can get the pump tested but it would be pretty pointless,if it is tripping the RCD it must have an earth fault.They are not repairable.
 
The fuse is unrelated to the tripping. It will likely trip again.
It is possible that the pump may be OK and there is a fault in the wiring to the pump which trips the RCD when it gets wet (rains). Check any connectors or joint boxes. All must be in watertight enclosures. PVC tape doesn't cut it.
 
is that all you did changed the fuse bs1362?
doesnt make sense why the rcd would trip you say everything goes upstairs/downstairs socket is this all on one rcd? could be accumlative leakage?
 
Last edited by a moderator:
Last time I saw something like this the pump would pump for a few minutes and then trip the RCD. Turned out the pump was faulty and it was about 5 years old. New pump fitted and problem resolved.
 

Reply to Pond pump still tripping rcd in the Australia area at ElectriciansForums.net

Similar Threads

I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock