My pool pump (230V 1Ph cap start) US Motor k63cxdfw-5159 ) wasn't working so I started to look for a reason. I found the terminal to the output control relay in the Intermatic program timer/ freeze control was burned off. None of the terminals were insulated and very close to each other and found a skeleton of tiny lizard in the wiring area. So I figured the lizard shorted the terminals together. I removed the output wires and tested the relay and got 230 across the DPST contacts as expected so I knew the relay was good. I replaced the terminal with a fully insulated flag, reconnected the wires thinking that would fix it. But when the timer turned the pump on, the motor sparked and smoked and tripped the breaker. I took a Ohm reading on the motor and read .06 ohms between the L1 and L2, and 1.61 ohms between L1 and ground, and 1.61 ohms between L2 and ground. Do these reading indicate the problem? What other tests can I do to the motor and wiring to fix the problem? Thank you in advance for your educated opinion.
 
!
Do these reading indicate the problem? What other tests can I do to the motor and wiring to fix the problem?
If you really mean 0.06 ohm between L1 and L2, you seem to have pretty well a short circuit across the motor winding.
What are you measuring it with - a digital multimeter?
Have you tried checking the capacitor (disconnected) is not short-circuit?
I would hope with the pump disconnected, there's no continuity between L1 / L2 and the case of the unit!!

If the wires directly from the motor measure such low values, it sounds like the motor is shot, but worth disconnecting it to make sure the control circuit is not introducing the problem.
 

Reply to Pool pump test procedure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need advice regarding an electronic problem on my Hayward Power-flo Matrix pool pump. I notice that : 1. Neutral wire from source has become...
Replies
4
Views
2K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I have a 4-wire well pump (red, yellow, black, and green) which just quit. Cycling normally, then shut off and never came back on. I've gathered...
Replies
3
Views
659
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock