Has anyone ever encountered a fault with a RCD which causes a potential on earth in respect to neutral?



I am a trainee electrician, working with an experienced electrician. We encountered a fault today, earth had a potential of 238V in respect to Neutral and a 0 V potential in respect to line.



We did an insulation resistance test at 500V on all circuits from line to neutral, line to earth and neutral to earth. All circuits gave a resistance of >999M ohm. So there is no way line and earth can be crossed anywhere.



The fault didn't trip the RCD or the MCB, yet there was a potential difference between neutral and earth.



We got really strange voltage readings while probing around, differences between earth and neutral ranging from 100v to over 300v, how can this be as nominal voltage was 238V.



The potential difference between neutral and earth was greater when the RCD was in the closed position.



All I can possibly think of is the somehow the line windings around the iron core in the RCD have made contact with the Neutral windings. Could a fault like this possibly create a voltage on Neutral, and cos it is a TN-C-S system, Neutral is connected to earth at the incoming supply, so is it possible this voltage could be seen on the earth bar in the consumer unit?
 
Hi dude,no guess would be possible,without knowing where you were measuring this voltage,and what position all the various switches/breakers,etc were in.

Start from a position upstream,where all measurements are as expected,or if not,somebody has a bigger problem :)
 
I just would like to know if anyone thinks it is remotely possible a fault inside the RCD could cause this issue?
 
You've posted this on another forum.

Why didn't you test Ze?

Yes I got a temp ban on this forum, so I joined another one. You use two forums too, else how would you know?

We didnt suspect the issue to be with the distributor.
 
Sounds like a floating neutral to me.

With the earth connected to the DNO's incoming earth, what resistance are you getting between N > E
 
So Gigsy..... are you going to update this forum with your findings reported on the other forum?

Is that necessary? I don't think anyone would be interested? Is it frowned upon to use two forums? If so why do you use more than on forum? Which forum do you like the best? Why are you making an issue with me using two forums?
 
People are free to use as many forums as they wish, All I would say is it's a bit like the first rule of the Fight Club.
Everybody knows the first rule of the fight club Right!!!!
 
Is that necessary? I don't think anyone would be interested? Is it frowned upon to use two forums? If so why do you use more than on forum? Which forum do you like the best? Why are you making an issue with me using two forums?

I think you're a bit of a pillock truth be told. No wonder you've already served a ban here, every post you've made has an air of arrogance about it. Go use the other forum, you serve no purpose here other than to annoy and irritate.
 
 

Reply to Potential difference between Earth and Neutral in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
565
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock