Hi All I’m new to the forum thing so go easy on me ;-)

if I am planning on putting a garage unit into my shed which will have a 32amp for power and 6amp for lighting is that OK to be fed from a 40amp breaker from the main board in the house ?

I didn’t know because of discrimination if I could just put the garage unit on an MCB ( which is in an RCB with one half of the circuits from house ) or if the shed circuit ( distribution circuit) would need to be on a Separate RCB/RCBO.

I know if there is a fault in the shed then the shed RCD would trip but if there was a fault between the shed and the main CU it would trip the house RCD.

If the Shed has to be on an Separate RCD then that would mean using an RCBO and since it just an RCD board I would need to replace the house board to be an RCBO board.

hope that all makes sense. Hope someone can shed some light on this.
 
Hi All I’m new to the forum thing so go easy on me ;-)

if I am planning on putting a garage unit into my shed which will have a 32amp for power and 6amp for lighting is that OK to be fed from a 40amp breaker from the main board in the house ?

I didn’t know because of discrimination if I could just put the garage unit on an MCB ( which is in an RCB with one half of the circuits from house ) or if the shed circuit ( distribution circuit) would need to be on a Separate RCB/RCBO.

I know if there is a fault in the shed then the shed RCD would trip but if there was a fault between the shed and the main CU it would trip the house RCD.

If the Shed has to be on an Separate RCD then that would mean using an RCBO and since it just an RCD board I would need to replace the house board to be an RCBO board.

hope that all makes sense. Hope someone can shed some light on this.
2 RCDs on the same leg is not a good idea, this is a private job other than your full time employment I have assumed???
 
I know if there is a fault in the shed then the shed RCD would trip but if there was a fault between the shed and the main CU it would trip the house RCD.

A fault in the shed will trip the RCD in the house if it is connected to it, the RCD in the shed will also probably trip.
 
Could you get a SWA to the shed? Are you able to calculate the appropriate size?
 
Is this job op, are you work for a company or your self ?

im just starting out this job will just be for my dad
[automerge]1580765223[/automerge]
Could you get a SWA to the shed? Are you able to calculate the appropriate size?

It’s for my dad and he already has 16mm2 , this is overkill but might as well over egg it than under egg it.
[automerge]1580765265[/automerge]
Don't put RCDs in series. What size/type of cable are you using?

SWA 16mm2
 
if there is room on the fuseboard, you could add an MCB between the main switch and the RCD to feed the shed. 32A would be fine.
then into the shed fuseboard which would have it’s own RCD feeding the sockets and lights.
should a fault occurs the shed, it will trip the shed rcd, not the main house one and visa versa...
 
if there is room on the fuseboard, you could add an MCB between the main switch and the RCD to feed the shed. 32A would be fine.
then into the shed fuseboard which would have it’s own RCD feeding the sockets and lights.
should a fault occurs the shed, it will trip the shed rcd, not the main house one and visa versa...

Great thanks this is helpful and think it is the way I will do it. We have enough SWA to go from the utility to the shed but not the main board so would the follow be OK.

1. A 16mm2 T +E from a MCB at the main board( not RCD protected ) the 16mm2 T+ E will then go through the house to the Utility.

2. 16mm2 T+E will then be joined inside the house utility to a SWA 16mm2 up to the shed. It will be joined via A separate main switch with will be on the wall inside.

3. Once joined the SWA will lead to the shed board which will be RCD protected.

I no ideally you would have an SWA from the shed to the main board but we already have the cable so will joining it via a separate main switch at the back of the house utility be acceptable ?
 
But does it meet the requirements for not having RCD protection?
Yes - Apart from the fact it would be connected to the SWA which does run outside ( which when a cable is used in the garden it would be require an RCD) but then again the termination won’t be outside as it would terminate in a shed.

otherwise I guess it would be better to run the cable from RCD protected inside and have no RCD in the Shed ?
 
Yes - Apart from the fact it would be connected to the SWA which does run outside ( which when a cable is used in the garden it would be require an RCD) but then again the termination won’t be outside as it would terminate in a shed.

otherwise I guess it would be better to run the cable from RCD protected inside and have no RCD in the Shed ?

I'm not sure you've fully grasped the requirements for RCD protection.
 
I was meaning the 'less than 50mm depth ' rule.

95% of the cable runs through the floor not in the walls so the 5% that does run down the wall to the where it joins the swa via a separate main switch , I will make sure either it is 50mm back in the wall or it has mechanical protection. Apart from that I think it’s fine yeah ?
 
1. A 16mm2 T +E from a MCB at the main board( not RCD protected ) the 16mm2 T+ E will then go through the house to the Utility.

2. 16mm2 T+E will then be joined inside the house utility to a SWA 16mm2 up to the shed. It will be joined via A separate main switch with will be on the wall inside.

Why on earth do you want to join it using a switch?

And why extend it with T&E?
[automerge]1580849657[/automerge]
95% of the cable runs through the floor not in the walls so the 5% that does run down the wall to the where it joins the swa via a separate main switch , I will make sure either it is 50mm back in the wall or it has mechanical protection. Apart from that I think it’s fine yeah ?

What is the wall made of? If it's a solid wall how are you going to cut a deep enough chase without damaging the structural integrity of the wall?
 

Reply to Power to Shed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
990
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
932
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock