Discuss Power track in offices in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
644
Giving a hand to some sparks on a real nice job..but..
Anyone fitted the power track system,bus bar & the plug off’s to sockets.
It states they are 3 metre lengths,if over then these leads need to be fused.
It’s a 63 amp system,with a 40 amp Rcd,also plug in 1.5mm flex,can’t get my head around this.
It’s all factory made,& all the bits have been sent,but why a 40 amp Rcd protecting the cable.
So it’s 63 amps,leads are 4.0mm straight from plug off,then 1.5mm of the Rcd.
 
I think the power track we installed had a 32A protective device feeding the track and the floor boxes had 4mm from the box to the plugin installed inmetallic flexible conduit.
 
Thanks all,yes the Rcd is for the sockets,I think the Rcd will need to be changed from 40 to maybe 32 or 16 amp.
Especially with the 1.5mm supplying sockets.
 
As above, what's the reason for down rating the current of the RCD?
 
This is the sort of equipment,this plugs straight into the 63 amp bus bar system.
 

Attachments

  • 9A16E689-3A7C-467F-9D98-9A073C150EC1.jpeg
    524.3 KB · Views: 15
look at my post regarding earth leakage, they might want to change there minds!!
 
So the 4 way is restricted to 12.6A effectively, I can't see 1.5mm having an overloading issue.
Ok,I personally haven’t seen something like this,this can be directly plugged into the Busbar,obviously the 3m length determinates the overload protection required.
@the moment this lead is actually on the Rcd module side,which is a 40amp rcbo,still not getting it though.
The Chiefs say it’s ok,it’s a factory manufactured plug & play.
 
 

Reply to Power track in offices in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
1
Views
227
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hey guys and gals. We bought a small office trailer that is wired up. It's never seen mains power and uses a generator disconnect (220). I read...
Replies
0
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock