Regarding 3 phase IR tests for initial verification, I'm wondering how people actually do it efficiently.

GN3 says to IR test between all phase permutations, then:
L1+L2+L3 connected together to N
L1+L2+L3 connected together to E
N to E

The OSG further comments that if the group test to earth is low then do each conductor individually to earth to find where the issue is.
So, two questions:
1) If anyone does it this way, how do you go about quickly joining the lives together, or have people made up special test leads with three probes/leads stacked for the purpose?
2) Isn't it just as valid, quicker, and simpler to IR test each phase to N and each phase to E instead of messing about joining them up? Anyone do this?
 

Julie.

Esteemed
Arms
Reaction score
4,539
If the wires are out, I earth everything except L1 then flash L1-E, then earth everything except L2 then flash L2-E, and so on for L3 and N - 4 tests complete each phase to phase, each phase to N, each phase to E, and N to E.

If all the wires are connected then I just bang through all 13 ways even though this repeats some tests
 

pc1966

Esteemed
Arms
Reaction score
11,027
If the wires are out, I earth everything except L1 then flash L1-E, then earth everything except L2 then flash L2-E,
I don't usually bother re-earthing already tested wires, so:
  • L1 - L2/L3/N/E
  • L2 - L3/N/E
  • L3 - N/E
  • N - E
If, for example, you have a L1-L2 fault it appears on the 1st test, so 2nd test you already know that pair are fine and don't need L1 to be earthed to check for it, etc.
 

Reply to Practical question about 3 phase IR testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
139
  • Question
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
507
Hi got my am2 Tomorow and not sure on how to test continuity for 3 phase circuits, like where to link out also for IR test aswell
Replies
0
Views
653
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
277
Been called to help a friend who can't get anyone to look at his car lift until next week and it's stopping him from working. I said I'd have a...
Replies
14
Views
1K

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top