I purchased a 7 day timer fused spur switch to replace a standard fused spur on a downstairs wc electric towel radiator. It seemed like it would be a simply swap out. However, it looks like the water supply earth bonding is connected into here and uses a thicker earth cable than the new spur switch can cater for, as the existing fused spur connections are inadequate. I have included images showing the existing spur switch and new timer switch and connections. Any suggestions on how I can resolve this? Choc blocks were originally there but the wago clips are simply there to protect the connections whilst I ponder a fix. Thanks for your help.
 
TL;DR
Replacing fused spur with timer version, but earth bonding in original spur! Help!

Attachments

  • 4E99FCBF-0E93-4065-8282-9E32A713910F.jpeg
    118.6 KB · Views: 24
  • 36652725-C6CC-4FD5-8C66-315166DF4AB4.jpeg
    97.8 KB · Views: 23
  • 34373681-C5F1-4BE6-BB54-604E4CA413A3.jpeg
    91.7 KB · Views: 23
  • 14F1363C-C449-4F9A-9289-9728F3DA8FC2.jpeg
    68.5 KB · Views: 22
You can put the 3 earth connections, plus one for the timer, into a 5-way level Wago connector. Possibly the smaller 221-415 type. Assuming the back box is big enough (or change it for a deeper one, if needed).

I did also wonder if this timer is a Class II device with an earth terminal for convenient only i.e. not actually needed, you could also check the instructions that came with it to see if that is the case. But in any case, the other 3 earths do need connecting together.
 
You can put the 3 earth connections, plus one for the timer, into a 5-way level Wago connector. Possibly the smaller 221-415 type. Assuming the back box is big enough (or change it for a deeper one, if needed).

I did also wonder if this timer is a Class II device with an earth terminal for convenient only i.e. not actually needed, you could also check the instructions that came with it to see if that is the case. But in any case, the other 3 earths do need connecting together.

Thanks for your reply. I will give this a try.
 
  • Like
Reactions: DPG

Reply to Problems fitting Fused Timer Spur Switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I have a switched fuse spur where the cooker hood should plug in to… above the actual cooker. I was wondering if I could swap this out for a...
Replies
7
Views
540
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
356
Wiring cooker hood into a switched fuse spur with a 13amp fuse in the spur. The cooker hood is 3amp. Should I swap out the 13amp fuse in the spur...
Replies
2
Views
299
Hi, I have ran a light ring off a fused spur with two lights on, each with their own switch (outside and lobby light) I want to put the outside...
Replies
4
Views
2K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
360

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock