Discuss Problems with IR test readings for my NICEIC inspection. in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

M

MisterX

Hi,
I'm having a bit of trouble getting my major works certs ready for the NIC chap to look at. My problem is my IR test results. I have replaced CU's in both my house and my parents house and just cannot seem to get a decent reading. Mum and Dad's Lights up/Down and Sockets up/Down all come back as 0.16Mohm.
I have only just done my Domestic installers course and am certain that i'm doing it correctly. All switches are closed and appliances and bulbs removed. When I join L+N and test them to E, I am getting >299 but individually they are low. Not too sure why i'm getting these readings on all four circuits.
My own house has readings of around 40-60 Mohms for most circuits but .36Mohm for my lighting circuit. I have a fan hard-connected to the light circuit in the downstairs bathroom so maybe thats it.
Any input you could give would be great as I'm desperate to get my major works certs up together and get registered so that I can eventually get started.
Cheers.
 
when you say individually,do you mean L/N?
 
When readings like this occur that are clearly unacceptable, the best action is to 'disect' the circuit and repeat the test. Disconnect them at the CU, go to the halfway point of the circuit and repeat the test. Then keep following in the direction of the low readings and you will eventually find the cause.
 
Widdler, thanks. I'll try that this weekend with mine but would you have any explanation why I would get the same 0.16Mohm on every circuit at my parents house. Seems odd!
 
i would suspect the testing, not the installation in that case. same faults on 2 sepatate installs seem weird
 
have you disconnected the circuits from the board and removed all lamps you could get low resaults if the lamps are in and the switches are on , an IR test should be carried out with the lamps out with the switch off and then with the switch on ,also any items such as PIRs ,fused spurs with neons in or electrical items that have not been un plugged will all give odd readings
 
Nick, My parents house is a 50's build and all of the sockets in that house have neons! Could this be the problem and if so, how do I get round it? Do I just record the LN-E reading? If so, would that be acceptable upon an NICEIC inspection?
Thanks again.
 
if you switch off all the sockets, the neons should then be out of circuit and that may be your problem
 
Nick, My parents house is a 50's build and all of the sockets in that house have neons! Could this be the problem and if so, how do I get round it? Do I just record the LN-E reading? If so, would that be acceptable upon an NICEIC inspection?
Thanks again.[/QUOTE
easyest way is to remove the tails N and L E joint the L and N together and test across them to the earth as you have said also check that nothing is plugged in and as telectirx has said ensure they are all switched off
 

Reply to Problems with IR test readings for my NICEIC inspection. in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
597
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
306
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock