Hi all, just wondering if anyone with a lot of experience had any thoughts on this;
I've seen on farms that are usually tt earthed the mains come in and through an s type time delay rcd and then sub mains go to different buildings which are protected by standard 30ma rcds. Sometimes faults in individual buildings will only trip the individual rcd but sometimes the main rcd will trip, losing power to all buildings.
would providing an earth spike for each individual building rather than just relying on one back at the mains improve things?
or is it just one of those things and using an s type rcd is all that can be done?
cheers
 
You shouldn't have 2 x RCD's of the same values in series, which is what your post suggests. Adding a spike at each building will not change anything.
 
As above, lower Ze wont make a difference, have you tested the time delayed RCD? cos if its faulty and not holding, you have whats described above 2No RCDs of same value and who knows which will disconnect first
 
Assuming you are talking about the time delayed RCDs being 100mA or higher then the only reason a time delayed RCD would trip before a non time delayed RCD is because of a faulty RCD or a simultaneous double fault.
There is the possibility of a time delayed RCD tripping as well as a single pole 30mA rcd and this would be on a neutral earth fault. To overcome this then you would need to use double pole RCDs.
Using multiple earthing systems across an installation would require careful though and planning but would not prevent the above scenarios. Because an RCD will trip on a Line Neutral imbalance, if the installation has a common supply, irrespective of the means of earthing, then any Line Neutral imbalance will be seen at all points in the installation upstream of the RCD.
 
well you should be getting discrimination between the 30mA and the 100mA s type..in favour of the s type..(thats the whole point of em)...

go get a leakage clamp on the origin...see how much leakage that s type is being subjected to...
 
Last edited:

Reply to Problems with more than one rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
225
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
715
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
471
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock