Have just completed a consumer unit change, Ze is reading at 0.09, PFC reading at 9.5kA, Its on a TN-CS System and about 150m from nearest transformer. I am not highly experienced in Testing, and unable to establish what is going on, but I am suspecting there is a big problem! I am using a Megger MFT1553, which is also tripping internally (as in displaying 'trp on the tester) when trying to carry out Zs tests across all circuits using the 'no trip' function. Any ideas??? :confused:
 
I have also tested the circuits using my Megger LT320 and it is displaying 'CHK'
Also have taken both Meggers to another house to eliminate equipment failure and both are functioning correctly.

I am panicking as the job is for my first ELECSA inspection next week!!! HELP!! :eek:

Im hoping its just my lack of experience missing something very simple!
 
When using the no trip function all 3 leads must be used. Make sure you have a good connection on all 3 for the full duration of the test. Can't see the Ze reading being of any relevance. Are all your R1 + R2 readings ok?
 
Have just completed a consumer unit change, Ze is reading at 0.09, PFC reading at 9.5kA, Its on a TN-CS System and about 150m from nearest transformer. I am not highly experienced in Testing, and unable to establish what is going on, but I am suspecting there is a big problem! I am using a Megger MFT1553, which is also tripping internally (as in displaying 'trp on the tester) when trying to carry out Zs tests across all circuits using the 'no trip' function. Any ideas??? :confused:

Hi mate,

I've got the same meter(1552) - the only time I've ever had this message was when I (foolishly) forgot that the no-trip loop test was a three lead test:eek:

I'd been trying to test with the two leads and it came up 'trp' each time.
 
I concur.

This is from the 1553 instruction manual.

Page10.jpg
 
Thanks for the replies, I have managed to get a Zs reading on my ring mains (using the 'plug' test lead) Im not sure why is it giving me a reading now, as before it was just stating 'trp' on the tester and not knocking out the RCD's. however, I have tried using the 3 lead method on my lighting circuits, as above, but it is knocking the RCD's out now! (I have been able to obtain a reading on my cooker radial using the 3 lead method though) Hmmmmm.....
 

Reply to Problems with Zs (and possibly Ze and PFC) Using Megger MFT1553 Tester in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi knowledgeable collective. To the chase. TN-S Megger 1553 2 wire Ze 0.09 but was getting Zs on cooker cable 1.5 metre long using No trip 3...
Replies
8
Views
976
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K
I've just carried out a periodic inspection on a building on an old RAF/USAF site. Commercial single story building. Wiring system is around...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock