Oh god! Here goes......

If = 230x0.95 (c min) / 0.36 (Zs) = 606 a

t = 0.1s (40a 60898 mcb)

K = 115 (copper line conductor) / 51 (steel armour) x 10 size of line conductor = 22.54

Sooooooo......

S = (sq root symbol ?) 606a 2 x 0.1/22.54 = 8.5mm

CSA of 2 core 10mm2 swa is 41mm2 so all is good?

Kill me now!
 
Last edited:
Did I not need to make the calculation for using different materials, copper and steel?
Thanks for taking the time spin I do appreciate it :)
 
Yeah, 0.1s is as low as BS7671 goes for your calcs, any Zs =/< max Zs for that 60898 would achieve that (as needs at least that fault current). As Zs drops, fault current increases and disconnection will get quicker. Would require manufacturer's data if you needed to go lower than 0.1s to satisfy thermal constraints but you definitely don't need to in the case of this job.
 
Hi - just FYI, from GN8 I read that 2 core swa 10mm has actual steel of 26mm (table B2). Since you only need 22mm (ish) steel to equal 10mm Cu (for thermal effects for 70C cable) then it’s fine.
Not sure, but your 41mm figure could be from 4 core 10mm cable?
 
Last edited:
Hi - just FYI, from GN8 I read that 2 core swa 10mm has actual steel of 26mm (table B2). Since you only need 22mm (ish) steel to equal 10mm Cu (for thermal effects for 70C cable) then it’s fine.
Not sure, but your 41mm figure could be from 4 core 10mm cable?
There are 3 different types of SWA cable.
70 degree C PVC 2 core 10mm2 BS6346 SWA has a CSA of 40mm2, and a value for K of 51.
90 degree C PVC 2 core 10mm2 BS5467 SWA has a CSA of 26mm2 and a value for K of 46.
90 degree C XLPE 2 core 10mm2 BS6724 SWA has a CSA of 26mm2 and a value for K 46.
 
When calculating the CSA of a protective conductor, using tabulated values, you use the tabulated values.
If you were calculating using manufacture’s data, you would use their values.
 
Last edited by a moderator:
There are 3 different types of SWA cable.
70 degree C PVC 2 core 10mm2 BS6346 SWA has a CSA of 40mm2, and a value for K of 51.
90 degree C PVC 2 core 10mm2 BS5467 SWA has a CSA of 26mm2 and a value for K of 46.
90 degree C XLPE 2 core 10mm2 BS6724 SWA has a CSA of 26mm2 and a value for K 46.
Hi - so are you saying that GN8 is wrong or that I’ve read it wrong? :) .
 
Last edited:
Am I missing something here?
If you know that the cpc is 26mm, why do you need to do the adiabatic?
Apologies if I'm being stupid.
 
Baddegg, genuine question - why use Cmin when calculating the fault current for adiabatic? Would this not give a best-case scenario lower fault current, where we would want a worst-case high fault current?
 
Good question pretty mouth, havnt used the adiabatic in real life scenario before so just went through my notes, this was a good opportunity to do some calcs and get the brain working agian as it’s my own property, I will be redoing it all this evening but as Andy points out it’s all a bit academic as we nlkniw the csa anyway.......possibly maybe :)
 
Hi - no questions can be stupid :) .

My thought is - the actual steel in 2x10mm swa is at least 26mm which when converted with the appropriate temperature rise k factors is equivalent to more than 10mm copper so it’s going to be ok for CPC. As you say, no real need to look at the adiabatic equation for that circuit.

Happy to have feedback if I’ve got this wrong :) .
 

Reply to Pros...cons...preferences.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
2K
I'm planning to build a shed in the far RH corner of the rear garden. It will have a reinforced concrete base, wood structure, flat roof and be...
Replies
0
Views
2K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...
Replies
15
Views
3K
I am considering the options which may apply to the earthing arrangement for a supply to a wooden shed. The property has a TN-C-S supply from...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock