Uksel - Just as the Nominal Voltage is oscillating then so is the Current - that's why its called "Alternating Current" as it flows in opposite directions each half cycle. It is therefore just as valid to describe the nominal voltage of the UK supply as 230V RMS as it is to refer to an alternating current of 100A RMS.

When using Ohms law to calculate an AC current flowing in a load as a result of an AC Voltage we replace "Resistance" by "Impedance". Impedance is a complex resistance which is related to how the load responds to an alternating current. The load's capacitance and inductance as well as resistance all contribute to its impedance. As capacitive and inductive reactance are related to the frequency of the alternating current/voltage then there can be a frequency dependence on the equation.

For PFC we assume that at 50Hz the impedance of the source (ie Ze) is a simple resistive value.

So Ipfc=Uo/Ze
 
Last edited by a moderator:
you need to disconnect the main incomming earth for a Ze test to eliminate the parallel earth paths, but the PFC (PEFC, PSCC) is carried out with the bonding in place.
 
Uksel - Just as the Nominal Voltage is oscillating then so is the Current - that's why its called "Alternating Current" as it flows in opposite directions each half cycle. It is therefore just as valid to describe the nominal voltage of the UK supply as 230V RMS as it is to refer to an alternating current of 100A RMS.

When using Ohms law to calculate an AC current flowing in a load as a result of an AC Voltage we replace "Resistance" by "Impedance". Impedance is a complex resistance which is related to how the load responds to an alternating current. The load's capacitance and inductance as well as resistance all contribute to its impedance. As capacitive and inductive reactance are related to the frequency of the alternating current/voltage then there can be a frequency dependence on the equation.

For PFC we assume that at 50Hz the impedance of the source (ie Ze) is a simple resistive value.

So Ipfc=Uo/Ze


Thread is 18 months old, 1-0 to me :p
 
Fellas. I thought a PFC was measured with the main earth still connected to the installation, line to earth, and a PSC line to neutral:confused:; only with a Ze do you disconnect the earth..

Fellas. I thought a PFC was measured with the main earth still connected to the installation, line to earth, and a PSC line to neutral; only with a Ze do you disconnect the earth..
 
Last edited by a moderator:
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF


This is a Ze you are doing a pfc Should be done with all earths and bonds connected as more paths to earth may mean a greater fault current as there is less resistance. Then test between line and N and take the highest amount. if you dont have that function do a loop test take the reading and divide 230 by the result. ie 230/ 0.26 = ka =0.884 ( 884 amps)
 
Well I was going to offer him this

[ame=http://www.youtube.com/watch?v=54C_FLSZaCY&feature=relate]YouTube - Prospective short circuit current test[/ame]

But then I noticed the date he asked,if he has not found out by now he has no hope
 
can somone tell me how to mesure pfc for a domestic property need this asap!!!!!
thanks in advance


Set meter on pfc

1 test between incoming line and neutral = PSCC

2 test between incoming line and the earth bar with all earths connected to include all parallel earth paths, not disconnected as suggested = PEFC

highest of 2 is recorded as pfc

can somone tell me how to mesure pfc for a domestic property need this asap!!!!!
thanks in advance


Set meter on pfc

1 test between incoming line and neutral = PSCC

2 test between incoming line and the earth bar with all earths connected to include all parallel earth paths, not disconnected as suggested = PEFC

highest of 2 is recorded as pfc


NB only Ze is measured with the main earth disconnected and installation isolated
 
Last edited by a moderator:
Thanks Laney06, never done it this way before, always used tester, how do you know this is correct, if it is this is easier and saves the cost of a loop impedance tester. tony
 
I have my niceic inspection tomorrow and would like to know how to calculate your cable length from the results you have measured on the cert? Can you help
 
I have my niceic inspection tomorrow and would like to know how to calculate your cable length from the results you have measured on the cert? Can you help


Probably the easiest way is to use your R1+R2 values and the stated values of resistance per metre for a particular cable, found in the OSG for instance.
 

Reply to Prospective fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
Replies
7
Views
1K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
386
I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
225

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock