Mike Me Mate
Hi I'm looking for some advice and options. I have installed a new board a British general one the customer has bought. I also got the meter cut out upgraded with a main switch put in.
At the main sw the pscc is 17.8, pefc is 6k
Which seems funny to me cause tncs which I'm sure new cut outs to be should be the same.
It's a 100a 1361 typeII cut out fuse.
Any way at the board the pscc is 8.7 and pefc is 6.
The easy way to deal with it was to put in a10k breaker. However bg or Mk sentry do not make 10k mcbs. Is there any 10k mcb that fitt Mk sentry boards or is there another option?
At the main sw the pscc is 17.8, pefc is 6k
Which seems funny to me cause tncs which I'm sure new cut outs to be should be the same.
It's a 100a 1361 typeII cut out fuse.
Any way at the board the pscc is 8.7 and pefc is 6.
The easy way to deal with it was to put in a10k breaker. However bg or Mk sentry do not make 10k mcbs. Is there any 10k mcb that fitt Mk sentry boards or is there another option?