Discuss Prospective fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have recently had test readings as follows -
On a Fluke tester - loop test L/PE earth fault current 22.8 ohms but the loop test L/N was 0.14 ohms.
This points to poor main earth connection.
Should I report to DNO.
Have done in the past and after calling to test. They only test L/N and advise ok but direct Zs at light point fails with high reading.
Any help with this please.
Your results for a TNS are understandable, you have an adequate neutral path hence your PSCC is fine, but you are correct in your assumption that the main earthing is not well hence the crap PEFC and Ze.
Get the DNO out to fix it.
Cheers…………….Howard
http://www.electriciansforums.co.uk...cal-installations/9138-high-ze-value-tns.html
Read this 5yrs old but still has many valid points for you to consider and will save a drawn out thread..
Did you read that link before posting?? Right couple of charlies on there!! NOT exactly good advice to pass on when one, is just submitting to installing a TT system instead of insisting that the DNO provided a PME connection in accordance with the satutory duty to maintain a provided DNO earth!! lol!!
Reply to Prospective fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
hi, new to this forum and still training. During testing for prospective fault current at the point I get a bad reading, what ever that may...
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...