Should really be multiplied by 1.732 (square root of 3). He measured the potential current flow between neutral and each phase in turn, choosing the max. So between neutral and a phase that's what you could have flow. If however the fault was between two phases then you'd get roughly double the potential current flow. HTH.
 
Last edited:
(square root of 2) 3,3,3,3,. go to the back of the class TQ.
 
the highest pfc will always be between the lines some test instruments cant carry out a test between the lines and can be dangerous
so for 3 phase we measure the highest line to neutral value Ie PSCC from eg
L1 - N = 500A
L2 - N = 515A
L3 - N = 505A

so L2 - N is the highest now multiply by 2 to get the estimated
3 phase pfc = 1030A or 1.03kA
this figure errs on the side of safety ie the worst case scenario
as topquark says a more accurate figure is 1.732 which is the sq rt of 3 not 2 which maybe a typo on his part
 
I think one of the reasons they say double it is that the voltage can vary a bit over time anyway, so taking a static reading can have a (small) degree of error as it may not be the max voltage that's (often) present. IE you may measure when it's around 232V and maybe it goes to a max of 239V.
 
it was a typo or a beer related error, but i just couldn't resist it. LOL. :winkiss:
 

Reply to Prospective short circuit current test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
Hi All, I am currently learning about AC and DC supplied coil and have been given the scenario below. I understand the first few steps but then...
Replies
1
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi looking for some help about faults and symptoms and difference between short circuit, dead short, and overcurrent to know which fault you have...
Replies
6
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock