Do I really need 16mm SWA to supply an external garage with a 63A 16A Power 6A Lighting unit? Maximum demand would be 100% of 16 + 40% of 6 which = 18.4 rounded to 19. Current carrying capacity of 16mm is 64A although its like £7pm. Or am I getting confused. Should I be saying that the maximum demand is 63A?

It's a TT installation which will have the garage distribution circuit protected by a 32A MCB and then downstream the 63A breaker in the garage has a 30ma RCD protecting the sockets. Upstream there will be a 100ma Time Delayed RCD which will be fitted inside the consumer unit, making the RCD the main switch.
 
First off RN what do you envisage being plugged into these sockets that is going need 19amps of load? That is totally over the the top unless your using a welder???

With just a 32amp MCB protecting your sub main, the 63amp part of your clacs are a little superfluous don't you think?

The 63amps is the rating of the load the RCD can withstand, in the same way an 100amp Double pole switch is rated at 100amps .............but rarely does 100amp go through one

Now a more realistic loading in this set up IMO would be 4-8amps maximum at any one time .............so what size cable do you think you will need.

Once you size a cable on your load, length of run, installation method etc, add say 3-4 more amps for the just in case factor/anything that you might want in the future/perhaps you want a heater in there in the chilly months .
 
Re: SWA size for garage sub..again!

First off RN what do you envisage being plugged into these sockets that is going need 19amps of load? That is totally over the the top unless your using a welder???

No welder, but sometimes I use a Table Saw, Mitre Saw although never usually at the same time.

With just a 32amp MCB protecting your sub main, the 63amp part of your clacs are a little superfluous don't you think?

Yes

Now a more realistic loading in this set up IMO would be 4-8amps maximum at any one time

Fair enough, but the lighting circuit powers 7/8 tubes as well. I appreciate not much more.

so what size cable do you think you will need.

Maybe 16mm was a little over the top, going on what you have just said and looking at table 4d4a in the regs I could use 6mm 38A CCC minimum with a 32A MCB, which could be a 20A MCB given what you've just said. My only question would be, is 6mm cpc enough? I guess 10mm would be more substantial.

Once you size a cable on your load, length of run, installation method etc, add say 3-4 more amps for the just in case factor/anything that you might want in the future/perhaps you want a heater in there in the chilly months .

Length of the run is approximately 18m. 60% buried.

:smiley2:
 
1. Unless it's a commercial type saw/mitre what are you look looking at watt wise 700/1000?

3. If fluorescent tubes then what 7/8 X 24watt or even 56watt that would be 448watts at the upper level and most likely HF so really 2/3 amps maximum

4. You can lay your pension/mortgage/and everything you own if your LIVES are 6mm then your 6mm CPC will be sufficient. But you could always use the Adiabatic

5. Even if you take it your permanent load is 15amps, remember we use Ib and not In then your vd on a 6mm cable @ 18mts would be less than 2 volts. So 6mm would be fine IMO
 

Reply to Protection against corrosion in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
880
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock