Discuss Protection on Tncs / tt system in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
644
Pme Swa sub main supplying external tennis courts.
Because of cable size,tt system will be installed.
The original Pme supply comes from main distribution area,from a Bill Switchfuse isolator,63 amps.
The new tt system is ze 13 ohms,the Pme earthing system is 0.35 ohnms.
No connection to the Pme system exists in the new install.
The wire netting around the tennis court as zs of 11 ohms.
All main bonding completed
With the metal DB what would happen if the live had an earth fault to the tt system,there is no Rcd protection @ present on the Swa supply.
 
The sub main if supplied via a TT arrangement will require fault protection via a suitably rated S type rcd.
If your using a TPN DB downstream then I suggest you install DP rcbos as a neutral to earth fault will disconnect an upfront rccb unless you use DP rcbos.

What is the issue regarding cable size?
 
The sub main if supplied via a TT arrangement will require fault protection via a suitably rated S type rcd.
If your using a TPN DB downstream then I suggest you install DP rcbos as a neutral to earth fault will disconnect an upfront rccb unless you use DP rcbos.

What is the issue regarding cable size?
Assuming his submain is using the PME the s type rcd would have to be at the point it converts to TT.
 
What size is the swa?
Why is the armour not suitable as the cpc, is it because of extraneous conductive parts at the tennis court building end?
 
Y
Nothing

Ze of 13 ohm, fault to earth then nothing will happen unless rcd protection is provided. It will remain live as your fault current is about 18A.
[/
What size is the swa?
Why is the armour not suitable as the cpc, is it because of extraneous conductive parts at the tennis court building end?
yea,16mm 3 core Swa,the main earth bond to the existing building is 50mm earth cable
 
Nothing

Ze of 13 ohm, fault to earth then nothing will happen unless rcd protection is provided. It will remain live as your fault current is about 18A.
Will look @ Fault charesteristics of the protection device.
Concerned if the fault happen on the tt system,the fuse would not protect.
 
This is the same problem as with meter tails in an Amd. 3 domestic CU on TT. The only thing that is not protected is the line upstream of the RCD going down to the TT earth. Could solve by putting RCD in separate insulated enclosure at tennis court end so that by the time the cables enter the DB they have local RCD protection. Can't do that in domestic install hence the magic glands etc to minimise risk of short.
 
This is the same problem as with meter tails in an Amd. 3 domestic CU on TT. The only thing that is not protected is the line upstream of the RCD going down to the TT earth. Could solve by putting RCD in separate insulated enclosure at tennis court end so that by the time the cables enter the DB they have local RCD protection. Can't do that in domestic install hence the magic glands etc to minimise risk of short.
Thanks,exactly what I was trying to say.
 

Reply to Protection on Tncs / tt system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
848
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
492
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock