Well, its not actual a cooker circuit but didnt know how to title it.

Its a circuit to a long plate warmer thing.. being used for a sunday carvery. Its 6.3 kw

There is a Submain in the pub kitchen, with few sockets, lights and extractor. it looks like the submain is fed by 10mm swa, 125a Main switch, with NO RCD protection.

Theres a spare way in the board so i planned to put this new circuit on a 32a MCB using 6mm T&E. This will be trunked down the surface of the wall prob 4ft from the bottom of the Submain. Then into isolator then onto a the 230v socket.

Am i right in saying this circuit will not need RCD protection as its surface mounted? is there a reg im forgetting?
 
The circuit is not for sockets not exceeding 20 amps
Its not buried cable less than 50mm without mechanical protection
Its not in a bathroom
Its not a TT system. Is it?
Its not mobile equipment not exceeding 32 amp for outdoors


I think thats most of them so,
If you compare the circuit to the above,I would say no RCd required



The instructed person get out clause is mainly used for the 20 amp socket item for commercial/industrial situations
 
The circuit is not for sockets not exceeding 20 amps
Its not buried cable less than 50mm without mechanical protection
Its not in a bathroom
Its not a TT system. Is it?
Its not mobile equipment not exceeding 32 amp for outdoors


Its a soket outlet above 20a (Being 32a) So is that NO RCD ?
I dont think its a TT, Ill double check. If it is a TT then it should have RCD protection no matter what ? right
 
I am assuming the existing DB in the kitchen is single phase

I think I would be checking the sub main calcs for an additional load of this size may be worth putting a clamp ammeter on the sub main to check existing load
 
Put it on rcd but if the say that they are skill or instructed and they sign some paperwork whick you would draw up and keep a coppie then you will not have to install rcd.

This is what nic said to me because i work in industriall and he said i should cover myself for no rcd protection.
 

Reply to PUB... Cooker Circuit ? in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock