What's your supply voltage is more importaint.

An what do you mean rated at 440V? As in that's the maximum voltage the starter will take?

What kind of starter is it?
 
What's your supply voltage is more importaint.

An what do you mean rated at 440V? As in that's the maximum voltage the starter will take?

What kind of starter is it?
For the OP, you also asked about how you should start the Motor, you need to take in lots of variables, mechanical loading for example, starting currents etc many things need to be considered.
 
Dependent on how big the pump is, and how much head pressure it has to overcome is another factor.

May also need soft starting/stopping to avoid "water hammer" in the pump/ pipework valves etc..
 
You will have to run in star. However the voltage is still a bit high.

Would be better with a VSD that you could trim the output to what you require.

Manual for soft start is here:


I should add, you're starter isn't rated at 440v it's 380 - 415 V.

What is your supply voltage?
Yup, you're right, sorry 'bout that, supply voltage's 400V, star indeed.. Thanks mate! Just wanted to confirm before doing it.
 

Reply to Pump Control in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello! I have a diesel fire pump and jockey pump. The Article 695 by NEC is only for ELECTRIC Motor Fire Pumps? For diesel drive, the control...
Replies
0
Views
306
Hi, I’m Not getting enough torque on startup to turn pump. Turns pump successfully maybe 1 in 6 times on startup and then fine at full speed...
Replies
9
Views
1K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi. I have a single phase water pump which supplies our house. It frequently cuts out and needs to be reset (on pump itself). Because of our...
Replies
3
Views
457
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock