gazdkw82

-
Arms
Reaction score
739
Connected up a showermate pump for a friend this evening. A plumber friend installed the pump a few months ago into the system, I just put a supply to it

Wired a FCU spur from a RFC socket in landing. Tested the circuit. All is good.

Energise the circuit. All good.

Open the tap to enable the point to run, RCD trips.

I knew it had to be something with tbr pump so I did a continuity test on it. There is continuity between neutral and earth. The cable is a pre wired flex.

Am I missing something, it's been a very long day....
 
I guess there could be some kind of filter on the supply which may manifest as continuity (can't remember exactly how filters manifest - could be if you keep the tester connected for a while it will disappear as the caps in the filter charge and the current flow stops - I'm sure someone will correct me if I'm wrong).

But based on what you've said, if there is a connection terminal box or something similar I might be inclined to open it (if it doesn't void the warranty) and see if it's possible to test the windings of the motor separately.

If you've got an el clamp meter, I might see if there is excessive leakage on the RCD that trips, possibly ramp test it, but I think my focus would be on the pump. Possibly do an IR test at 250v... L-N, L-E and N-E, but if there is a filter this would skew the results.
 
When you say there is continuity between N and E, exactly how many Ohms (or MOhms) did you measure?

Could well be faulty internal wiring or a short - I once had a new downlight from a well known brand with a N to E fault due to a screw having penetrated the N cable in the internal rubber potting compound.
 
If you've got an el clamp meter, I might see if there is excessive leakage on the RCD that trips, possibly ramp test it

Just to clarify... there is obviously excessive leakage because it trips, but what I mean is to try and establish whether say the RCD trips at 26mA and without the pump it's sitting at say 25mA.
 
I didn't have a low ohms meter, just a meter to bell out.

I think the issue must lay with neutral to earth seems the rcd trips only when the tap is opened (enabling the pump to run). As soon as the pump tries to run (I.e a load) it trips RCD.

It's got neutral to earth written all over it?
 
Most pumps use reed switches to switch relays to turn the pump on. Might be live to earth after the pcb inside. If N-E it might trip the rcd with a load on the RFC?
 
If there is a permanent N-E conductive path at the pump or in the new wiring you have done, then while the FCU is closed other loads might be expected to cause the RCD to trip when they switch on. Have you tried using a vacuum cleaner on the ring plugged in close to the point you spurred off to see if its starting surge causes the RCD to trip? If it does, open the FCU (FCUs are double pole) and see if the vacuum cleaner now causes the RCD to trip. Try turning on the vacuum cleaner a few times in each case of FCU closed/open. This little trial may gives you some pointers. (I assume the pump is functionally switched in the line only).

As an extra did you bond together the inlet and outlet pipes if they are metal with 4mm2 or thicker? If not there could be some strange earth leakage current flows when the pump is run because the inlet and outlet pipes are different potentials.
 

Reply to Pump wiring issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Replies
17
Views
596
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
382
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
642
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
904
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
291

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock