Joe S

-
Reaction score
17
I have been asked to Supply & Fit a Pure Sine Wave Generator to a solicitors office for 1-2 days while the main gets switched off in the road for a building development alteration. They have been told by their IT guy it has to be a certain kind of generator due to the computers.

The Install is a 100a TNCS supply a. Henley Block which then supplies 4 other smaller boards. The total demand of all of the boards is 64.8A combined. Obviously they can run a Skelton type operation for a day or two to keep the load usage to a minimum.

I was thinking of installing an Ip rated enclosure with a 40a rcd and earth rod outside by the generator and then running a sub main to the Henley block. I was also going to put the mains tails into their own Henley block for the duration of the works so as not to have two supplies running together if they turn the power back on early.

Does this sound the right thing to do as I've never had to install a temp generator before? Also, where is the best place to hire them as I can't seem to find one at least 6kva?

Thanks in advance.
 
There are loads of Generator hire companies, whether you have one near you i wouldn't know, but i'm sure there used to be one down that way in Kent.

You'll be hard pushed to find a gen-set suitable for IT of that low rating, far more likely to be over 10 KVA. And yes, you will need a temporary earth rod, as you could well be losing your main earth as well as power... Give the gen hire company full details of your requirements (IT load etc) and they will be able to provide a generator suitable for your purposes, and will even provide you an installation guide for your requirements etc

Install a suitably sized switch fuse isolator, via henley's and use the existing CU/DB RCD's. Just make sure that if DNO supply does return unannounced, it stays at the service head.
 
Never mind loosing the DNO earth, the earths have to be separated. It sounds like the DNO are working on the cables so there’s a danger of exporting a fault and injuring cable jointers.
You need to contact the DNO and as well the hire company.
 
It's probably the DNO that have advised these businesses they need to make alternative arrangements. Normally they would be providing the temporary generator supply, ...it's normally the case anyway, if the disruption of power is for the suppliers benefit or for fault repair over an extended period (8 hours).

Anyway as far as the earthing is concerned, only the incoming main earth (TN-S/TNC-S/PME) needs to be removed/disconnected and isolated from the MET, and replaced by the temporary rodded earth.
 
And what stops back feeds in to the incoming supply? Both Ph&N need to be disconnected at a centre off change over switch.

This would be taken care of with a separate Henley to keep the mains tails away from the installation and generator.

I shall check with the solicitors about the supplier providing temp power.
 
I have been asked to Supply & Fit a Pure Sine Wave Generator to a solicitors office for 1-2 days while the main gets switched off in the road for a building development alteration. They have been told by their IT guy it has to be a certain kind of generator due to the computers.

The Install is a 100a TNCS supply a. Henley Block which then supplies 4 other smaller boards. The total demand of all of the boards is 64.8A combined. Obviously they can run a Skelton type operation for a day or two to keep the load usage to a minimum.

I was thinking of installing an Ip rated enclosure with a 40a rcd and earth rod outside by the generator and then running a sub main to the Henley block. I was also going to put the mains tails into their own Henley block for the duration of the works so as not to have two supplies running together if they turn the power back on early.

Does this sound the right thing to do as I've never had to install a temp generator before? Also, where is the best place to hire them as I can't seem to find one at least 6kva?

Thanks in advance.

so this means no scams & partP5WWkevs then....
 

Reply to Pure sine wave generator temporary install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
493
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock