bf2k

Active EF Member
Messages
25
Location
East Lancashire
Hi, I'm relatively new to this forum and have not long since qualified.

As one of my first job, I recently installed a new CU to feed a large shed. I got the clients provider out to install a service switch so I could safely tail up the new CU. Whilst the engineer was out he plugged his tester into one of the house sockets and found there was no earth. After I'd finished the shed feed I looked at this problem and have uncovered a much bigger problem.

The existing CU is the original from the 70's, standard 3 way re-wirable Wylex box with a 5 AMP and 2x 30 AMP fuses. The lighting circuit is working fine. One of the 30 amp circuits is a radial with a 4mm cable, but I don't know where it is running to. But the 30 Amp circuit I have the problem with is for the house socket ring main (which had no earth). After removing the socket (which to begin with I thought it was a fault with the socket as the rest of the circuit was fine) I found that the earth connection was loose. However, I did the standard IR test on the circuit to issue the minor works cert where I found that there was a problem. My meter (fluke 1653) wouldn't even give me a reading. I've tried doing the test on both 500 VDC and 250 VDC, where both gave me a 0.00mohms reading @ 0.8VDC (which has puzzled me). So I did an R1+Rn gave 53.4ohms (R1+R2 and R2+Rn give >2000ohms). So from this I thought they must be a short between Live & Neutral and proceeded to fault find.

I split the circuit, found faults on both sides. So I split each side and have now managed to narrow this down to 4 sockets (the second in the line, one at the top of the stairs and 2 in the kitchen). What I'm puzzled at is no work has been done recently and the sockets which have faults don't seem to be consecutive sockets in the circuit. Plus before I changed the socket in the hall (which was the first in the line) the system worked. I also did a test from earth and neutral to a back box and got continuity, which again has puzzled me. I didn't do any tests other than the plug in tester to confirm what the engineer found before I changed the socket. They seems to be no logic to which socket follow the last and there are a few spurs running in a few places, but they seem to be fine.

This is the first fault finding mission I've had to do on my own since qualifying and I think I've been dealt a real one. Its a good job I know the client. I guess they can't prepare you for things like this at college.

Does anyone have any ideas, or come across something similar before?

Thanks
Andy
 

Marvo

Admin and gender confused
Staff member
Admin
Messages
16,214
Location
South Africa
It sounds like you're beginning to run around in disorganised circles.

As this is your first job I'm guessing you might not be completely familiar with your test equipment. You're misinterpreting the readings, if there was a L-N short then it would have been blowing the fuse.

Go back and start with the primary fault again (no earth). Find the missing earth and reconnect it. Don't start complicating the issue with other tests until that's done. Once you've fixed that you should be able to power up the installation as long as you haven't altered anything else.

Could the N-E low resistance be coming from the TNCS arrangement at the point of supply entry?
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
Thanks for the reply

I have re-connected the earth and done the appropriate test, all good. I have disconnected the Live, Neutral & Earth for the ring from the rest of the supply (plus I'm not getting a low resistance from N+E). As part of the minor works an IR reading must be taken, which is where I've found the fault. I don't really want to juice it up to be honest until I'm 100%.
 

Marvo

Admin and gender confused
Staff member
Admin
Messages
16,214
Location
South Africa
plus I'm not getting a low resistance from N+E
I'm possibly misunderstanding your tests, I got the impression you found low IR N-E when you said;
I also did a test from earth and neutral to a back box and got continuity, which again has puzzled me
 

ExArmy

Electrician's Arms
Messages
715
Location
cumbria
so what was plugged in when you measured your L-N 53ohms!?
just go through the test sequence for a ring main in order and then it will make more sense.
 

spark 68

Electrician's Arms
Messages
2,159
Location
UK
Hi Marvo,

I think you on on the money the first time, if it is TNC-S and only the fuse was pulled he would get N-E continuity, this reading would then disappear when the cable was disconnected at the source
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
This was done with a continuity tester (Fluke T100) between the back box and Live, back box and Neutral & back box and earth.

It was also that last test I did before light gave up on me.

The thing which is puzzling me is that the fault(s) is between these 4 sockets which aren't consecutive. Would you be powering up the circuit after re-connecting the earth even with the poor IR readings?

To reply to other posts:
Nothing is plugged in. I've unplugged all appliances and disconnected any spurs that are run off sockets (although this isn't saying there isn't anything under the floor)
 
Last edited:

valleybilly

Scuber Do
Messages
218
Location
Manchester
Your fitting a cu on a minor cert to a shed ? . Next time someone tells you there is another problem then tell the client directly , Your cuoriosity is comendable but it dont pay the bills tick tock mate lol ..
 

Strima

Electrician's Arms
Messages
3,634
Location
St Neots
TBH it might be worth lift a couple of boards to see if any DIY additions have been made, choc blocks etc can easily be hidden.
 

Strima

Electrician's Arms
Messages
3,634
Location
St Neots
One of the 30 amp circuits is a radial with a 4mm cable, but I don't know where it is running to.
Cooker/shower? Have you been in the loft? May have also been a radial for the old forced air heating systems so a socket/blanking plate near the airing cupboard may be a good place to look.

The first thing I do after a nice cuppa from the client is to identify all circuits, this can actually turn out to be an advantage and save you pulling cables through when there's already one there.
 

spark 68

Electrician's Arms
Messages
2,159
Location
UK
The first thing I would do is disconnect the entire circuit from the CU (including the N+ E ), then do the tests in sequence, and see where you go from there.
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
valleybilly - at what point did I say I was fitting a CU on a minor works? I think you'll find I stated it was a separate job and, quite correctly, I was doing the socket on a minor works.

Is it always this "hostile" on here or is it the time of the night?
 

Strima

Electrician's Arms
Messages
3,634
Location
St Neots
Don't worry about the locals mate, it's Friday night and and no one has pulled... :lol:
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
Thanks Strima

I've been in the loft and, although extremely full, only a light run off an upstairs light is up there. The shower was on its own CU, but has since been removed. The oven is run off a plug top to a socket on the ring main. The own of the house has been there since it was built and said she'd had storage heater before central heating, so I'll go and have a look under the floor boards near the boiler for a capped off supply. Lifting other boards in the house maybe tricky though. Its not a minimalists house if you get my drift.
 

Marvo

Admin and gender confused
Staff member
Admin
Messages
16,214
Location
South Africa
Lol, I think you've got some food for thought at the very least. It's difficult to give specifics because a lot of the tests you did are inconclusive and some of your results such as there 'a short between Live & Neutral' are contradictory if the fuses weren't blowing.

I would go back and as suggested completely disconnect any suspect circuits to eliminate any parallel paths and conduct all the tests again from scratch. If your tester gives any confusing or inconclusive results try the same tests again with an analogue tester.
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
Cheers Marvo

I'll give it another go tomorrow, more light and a fresher mind. I'll have to dig out my analogue multimeter from yesteryear as well.

Thanks (to most) for your help and ideas.
 

somersetsparks

Regular EF Member
Messages
1,251
A non textbook but useful way of fault finding a 'working' Ring, Is to disconnect 1 earth from the fuseboard, power back up, test at every point between L-E and see where you lose the reading, then change the earths over in the board and repeat the process, you can then narrow down between which points your fault(s) is. Obviously you should unplug everything first. You can also use this method for Live and neutral faults as well,
I wouldn't do it on a dead circuit that I knew nothing about, however this ones been in action for 40 years. The 53 Ohms is a certain load still connected (approx 1kW).
Fault finding out in the field is quite a skill and certainly different to classroom situations! Good luck and be logical and methodical!
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
A little update as i'm on site now. I've narrowed it down to between the socket at the bottom of the stairs and the socket at the top of the landing. No other socket is between these two points. I've got a 0ohms reafing for ir between these two points and 50.2 for continuity. These are between live and neutral. Live to earth and neutral to earth is fine. Before i lift floor boards had anyone come across this before?

Cheers
 

Brightspark2

Regular EF Member
Messages
1,978
Location
North West
Sounds like a load giving false readings...as said that type of fault would blow the fuse when it was energized...

Is there an RCD socket or neon?...there's light at the end of the tunnel now, keep looking...

Sent from my Xperia S using next doors WIFI.
 

snowhead

Respected Member
Mentor
Trainee Access
Messages
3,784
Location
Mildlands
No other socket is between these two points.

Cheers
Have you followed the cable, or are you assuming because you can't see a socket?

Spur for a burglar alarm, or old spur for wall mounted heater or socket under the stairs in a cupboard??
 

somersetsparks

Regular EF Member
Messages
1,251
Well that would be a load of 4.58A, so in theory would not blow fuses but would be a hell of a drain on finances! However Live to neutral faults are very rare in T+E installations, A connected load would be much more likely, being that its in the hallway, this would be the most likely place for a spur which could be anywhere in the house! Also, since this is a likely load connected I would be very careful meggering it further as you could end up buying some form of domestic appliance! That would be far more of a pain then the fault :wink5:
My domestic experience only extends to testing/repairs and fault finding and I have yet to find a genuine L-N fault!
 

Richard Burns

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
9,926
Location
Cambridgeshire
Cables from upstairs to downstairs can be damaged if they pass through the stair treads and are constantly trodden on, also are you sure that there is not something in the cupboard under the stairs as it is an easy place to spur from, tap in to get a light, etc.
1kW appliance sounds unlikely in that location but could be possible, or a failed accessory.
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
I've located the fault. A cable run just under the floor boards had worn. Replaced cable and all fine now on the live neutral ir front. However I've now lost continuity between the two ends of the ring. Going through everything I've done now but everything is connected correctly.

I've got a reading of 0.31ohms between neutral and earth (evetything is disconnected from cu). With this being an old installation this could be a bare earth touching a back box or neutral leg, is that a correct?

I'm going to connect a fly lead to each leg and go round to see if i can see where the live i as lost.

Pain in the arse these fault finding missions aren't they?

Ps all the meggering has been done at 250v incase of connected appliances ive missed.
 

Amp David

Mentor
Electrician's Arms
Trainee Access
Messages
5,113
Location
Glossop
If you had ring continuity before doing the repair, then it has to be your repair. Is it non continuous on each conductor?
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
Again an update for those who are interested.

The faults I found were, loose neutrals in a kitchen socket, a poor (very poor in fact) connection for the boiler - were loose strands were hanging out everywhere (British Gas so called fitters for you :innocent: ) and a broken cable under the floorboards were a wardrobe had recently been moved. All fixed and working.

But the biggest thing I found, which once realised made a lot of sense to my test readings, was that the sockets which were fed into the same 30A fuse labelled "Socket Ring Main" is actually two radial circuits. So I've de-rated the fuse to 15 Amp and moved one of the circuits to a spare fuse rating that at 15 amp as well as a temporary measure. I've notified my customer that if she uses too many appliances at once she may blow the fuse and that she really needs a re-wire and new CU. As expected she doesn't want the expense and mess of decorating. So I've said she really needs the circuits to be protected by a 20 amp fuse and have suggested replacing the re-wirable fuses with the plugin mcb's (its a wylex board). Because I found a short between earth/neutral I can't put rcbo's in so wondered if putting an rcd before the board would still work, although I think the short is happening between the installation and the building.

I suppose not finding that the sockets were if fact radials is due to a lack of experience and will be learnt from, not to take other peoples notation as gospel is one of them.

Thank to all that helped and allowed me to have a Sunday off for once :)
 

Strima

Electrician's Arms
Messages
3,634
Location
St Neots
Glad you sorted it mate, it's a good feeling in the end. An upfront RCD will still trip.
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
It does, especially when you flick the switch and plug your tester in and you don't hear snap crackle pop and get the results you want :)

I thought it would do but thought I'd look into the idea. I've told her that she really needs a new CU, which in turn will mean she needs a rewire (mainly because of the N+E fault and the IR between L+N was 8mohms. Must be puzzling for her though because the system has worked for 40 years. I've told her to go and get a second opinion if she needs but at least give me a chance to quote :). She has taken me up on the suggestion of recplacing the re-wirables with plugin mcb's.
 

Strima

Electrician's Arms
Messages
3,634
Location
St Neots
She has taken me up on the suggestion of recplacing the re-wirables with plugin mcb's.
Some people are even reluctant to do that. However I have pointed out the benefits even even just doing the lighting circuits so they're not trying to cram a nail in the carrier with a match between their teeth...
 

ayjay

Regular EF Member
Messages
1,194
Location
north korea
why not find the 2 ends of the radials and link them to form a ring,
then find the e/n fault and fix it
(btw what size cable are the radials ? some are 4.0 mill)
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
I've suggested that but she doesn't want to redecorate. Plus that would then be notifiable work and would need to comply, which it wouldn't because there is no rcd.

I've tried to find the E+N fault at each point and can't locate it. It is also in the lighting circuit. She doesn't want me ruining her house basically :).

It's 2.5mm^2 cable as well.
 
S

Ses2010

It does, especially when you flick the switch and plug your tester in and you don't hear snap crackle pop and get the results you want :)

I thought it would do but thought I'd look into the idea. I've told her that she really needs a new CU, which in turn will mean she needs a rewire (mainly because of the N+E fault and the IR between L+N was 8mohms. Must be puzzling for her though because the system has worked for 40 years. I've told her to go and get a second opinion if she needs but at least give me a chance to quote :). She has taken me up on the suggestion of recplacing the re-wirables with plugin mcb's.
Just out of interest why does a l-n ir reading of 8meg ohms make you think it needs a rewire?
Its still well within the allowable although low it still is acceptable.
Would it not be better to suggest finding the n-e fault and just a fuse board upgrade
 
G

Geoffsd

I've tried doing the test on both 500 VDC and 250 VDC, where both gave me a 0.00mohms reading @ 0.8VDC (which has puzzled me).
Just for information -

This is because the meter has detected the very low reading ( 54Ω in this case ) and stopped the test at 0.8V rather than go up to 250V or 500V which may damage equipment.



Also, you haven't mentioned end to end continuity testing of the conductors.

This should be the first test on a Ring and would have told you right away that it wasn't a ring - because it never was or that it was broken.
 
OP
B

bf2k

Active EF Member
Messages
25
Location
East Lancashire
Just for information -

This is because the meter has detected the very low reading ( 54Ω in this case ) and stopped the test at 0.8V rather than go up to 250V or 500V which may damage equipment.



Also, you haven't mentioned end to end continuity testing of the conductors.

This should be the first test on a Ring and would have told you right away that it wasn't a ring - because it never was or that it was broken.

Thank you for the info. Like I said, lessons obviously learnt and all down to experience.
 

ayjay

Regular EF Member
Messages
1,194
Location
north korea
bf2k--
take all of the sockets off of the faulty radial, and part the conductors--(its an old 70,s built, so there can,t be many sockets),
in the existing d/b, disonnect the l/n/e of that radial circuit, then test each leg,starting from the outgoing 2.5 twe then each loop to the last one, the final socket with only one cable
if you find some kind of fault on a leg trace it
 