Discuss Puzzling RCD Fault in the Australia area at ElectriciansForums.net

S

spadxiii1918

Hi, I need some advise or help on the following problem.
RCD failed trip test. Failed ramp test. and faield to trip out when Shorted between Earth and bus bar.
I had replaced the RCD with 3 other units, but still would not trip. (ELI 1.17 Ohms)3 lead test L N E and 2 lead test L-E (still no trip).
It did however trip from the supply meter tail side and earth
Power supplied by over head cables into loft to meter.
Replaced batteries to meter just to make sure
Any hep would bemuch appreciated.
 
Hi, I need some advise or help on the following problem.
RCD failed trip test. Failed ramp test. and faield to trip out when Shorted between Earth and bus bar.
I had replaced the RCD with 3 other units, but still would not trip. (ELI 1.17 Ohms)3 lead test L N E and 2 lead test L-E (still no trip).
It did however trip from the supply meter tail side and earth
Power supplied by over head cables into loft to meter.
Replaced batteries to meter just to make sure
Any hep would bemuch appreciated.

Could you clarify?
 
I agree with both previous posts it could very well be something as simple as supply and load tails reversed, keep us posted on how you get on.
 
Hi Guys,
fault turned out to be no earth, although we had an original ELI of 1.17 ohms. When the bonding was disconnected along with the main earth and an ELI taken from the incoming tails and presumed earth conductor the ELI was over 700 ohms.

I take it that the RCD could not "See" any fault as no current or fault was being detected.

Thanks for all your help on this
 

Reply to Puzzling RCD Fault in the Australia area at ElectriciansForums.net

Similar Threads

Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
356

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock