Discuss Pv tripping rcd in the Electrical Tools and Products area at ElectriciansForums.net
P
piz
Hello all,
I have been to a property with a crabtree starbreaker board main switch is 80A 30ma rcd.
The customer thought the dishwasher was tripping electrics I teste IR when I tested RCD it tripped on times half!
I have ordered a new one but when the breaker is turned off for the PV the rcd no longer trips, Would this be a PV fault been insalled over a year can we test them? (PV)
wht would it trip if only feeding?
Cheers
You may have got a better response posting in the solar photovoltaic forum rather than tools and products.
PV generates stray DC voltage on the AC side and can trip an RCD very readily. This is not a fault, it is characteristic of PV.
Normally PV is installed in such a way that it is not required to have an RCD on the circuit.
Check the installation method and see if the PV can be relocated on a non RCD circuit.
Whoever installed the PV system on a board protected by a single RCD has created a dangerous situation.
Many, if not all of the circuits protected by the RCD would be required to disconnect within 0.4s. A PV inverter can take up to 5s to shutdown which means than circuits could remain energised via the inverter for longer than their 0.4s maximum when the RCD trips.
I suggest that the PV system is removed from the upfront RCD protected CU, a separate 2 way CU is installed via henley blocks in the main tails and the PV is fed from that.
Reply to Pv tripping rcd in the Electrical Tools and Products area at ElectriciansForums.net
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...