Hi,
I've been having a nose through some of the old past Chief Examiner reports and the December 2011 edition has on page 5 has the following quote:

Many candidates were unable to identify the first three tests to be carried out on a newly installed ring final circuit, with many beginning with continuity of cpc followed by ring final circuit continuity. The tests are ring final circuit continuity, insulation resistance, earth fault loop impedance.

Can anyone explain why Continuity of CPC is not the first test? Is it purely because if you get an end to end reading on the CPC then that is sufficient as I thought you had to take a reading at every point???

Cheers guys!

http://cdn.cityandguilds.com/Produc...01_Chief_examiner_report_December_2011_v1.pdf
 
Because you are talking about a new ring final circuit the first test is the three step test to ensure ring final circuit continuity and determine R1+R2. Whilst it is possible that the first measurement you take is end to end of the cpc, this is only one section of the entire test: three end to ends, r1+rn, r1+r2 the latter two at every point of utilisation.
 
Because you are talking about a new ring final circuit the first test is the three step test to ensure ring final circuit continuity and determine R1+R2. Whilst it is possible that the first measurement you take is end to end of the cpc, this is only one section of the entire test: three end to ends, r1+rn, r1+r2 the latter two at every point of utilisation.


Im not saying your wrong but I cant work that out in my head.
The first test on a ring final circuit is:
Step 1:
r1 end to end i.e resistance of the line conductor from one leg to the other.
rn end to end i.e resistance of the neutral conductor from one leg to the other.
r2 end toend i.e resistance of the cpc from one leg to the other.
r1 and rn readings should be within 0.05ohms of each other.
Step 2:
R1 + Rn i.e connect neutral from one leg to the line of the other leg and vice versa (figure of 8) take the reading at each socket. The result should be (r1 + rn)/4.

Step 3:
R1 + R2 i.e connect line from one leg to cpc of the other leg and vice versa (figurs of 8) take the reading at each socket. The result should be (r1 + r2)/4.

If this is what you meant RB, then I apologise.


Jay
 
Im not saying your wrong but I cant work that out in my head.
The first test on a ring final circuit is:
Step 1:
r1 end to end i.e resistance of the line conductor from one leg to the other.
rn end to end i.e resistance of the neutral conductor from one leg to the other.
r2 end toend i.e resistance of the cpc from one leg to the other.
r1 and rn readings should be within 0.05ohms of each other.
Step 2:
R1 + Rn i.e connect neutral from one leg to the line of the other leg and vice versa (figure of 8) take the reading at each socket. The result should be (r1 + rn)/4.

Step 3:
R1 + R2 i.e connect line from one leg to cpc of the other leg and vice versa (figurs of 8) take the reading at each socket. The result should be (r1 + r2)/4.

If this is what you meant RB, then I apologise.


Jay
I am possibly guilty of assuming too much knowledge.
Your post is exactly what I said.

I may have missed some details but I was only referencing and not describing.
 
I am possibly guilty of assuming too much knowledge.
Your post is exactly what I said.

I may have missed some details but I was only referencing and not describing.

Like I said, I may have misunderstood. Then again, I have had two bottles of red. I'm having trouble p1ssing in the pot, let alone understanding a technical post. The post I put up was one I had written ages ago...lol I just copied and pasted...lol

Jay
 
Ahh ok I understand now. I guess the sequence of tests 'CRIPPLER' refers to the installation as a whole. By the same logic the sequence of tests for a radial wouldn't include the Polarity (Dead) test as this would have been confirmed already by the R1+R2 reading?

Cheers guys!
 

Reply to Query regarding old 2391 question - RE sequence of tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
808
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
630
Got a couple of sparkies doing the 2391 exams, now split to make it easier. Seen some of the questions exam sheet… interesting reading for us say...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock