Hi everyone,

I have what I'm sure is a very basic question that I would really appreciate some help on. I am a cider maker and recently purchased a new apple grinder that is manufactured in Germany and runs on 230v/50hz. I am wondering how I can use it here in the US? It came with a power supply that requires me to wire my own plug to it (not pictured below). But my question is, what do I need to do to make it functional here in America? Any and all help would be much appreciated. Thanks so much in advance,

jack
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
4,803
the rating plate says 50/60hz
220v is probably close enough for the motor to be run without problems.
you need a 220v outlet and a cable made up to connect it.
often your tumble dryer outlets are 220v if I recall?
 

Lucien Nunes

-
Mentor
Esteemed
Arms
Reaction score
9,965
Typical residential supplies in the USA are 120V / 240V split-phase with two hot wires and a neutral. Domestic appliances typically use one hot and neutral for 120V, but stoves, dryers, A/C etc use the two hots to supply 240V and this configuration will power your apple grinder.

You will need a 240V grounded outlet to plug the machine into; it does not matter whether the outlet has a neutral or not, as the machine won't need it, only the two hots and ground. Therefore either of the two common types of 240V receptacle, type 6 (without neutral) or type 14 (with neutral) will suit. Then you would make a cable from a matching plug, (e.g. if you have a 14-20R receptacle then a 14-20P plug) to Schuko inline coupler to fit the machine. The line and neutral terminals of the coupler will connect to the X and Y terminals of the plug. Because the inlet on the machine is non-polarised, it does not matter that both wires will be hot, instead of hot and neutral.

Larger 240V outlets such as 30A and 50A rated types used for stoves and dryers will supply the necessary power but the breaker will not offer adequate protection to the machine cable. You would need to down-rate the circuit to say 20A or add a local breaker box with a smaller outlet.

Ensure codes are met regarding ground fault protection if required.
 

Megawatt

-
Esteemed
Arms
Reaction score
1,172
Typical residential supplies in the USA are 120V / 240V split-phase with two hot wires and a neutral. Domestic appliances typically use one hot and neutral for 120V, but stoves, dryers, A/C etc use the two hots to supply 240V and this configuration will power your apple grinder.

You will need a 240V grounded outlet to plug the machine into; it does not matter whether the outlet has a neutral or not, as the machine won't need it, only the two hots and ground. Therefore either of the two common types of 240V receptacle, type 6 (without neutral) or type 14 (with neutral) will suit. Then you would make a cable from a matching plug, (e.g. if you have a 14-20R receptacle then a 14-20P plug) to Schuko inline coupler to fit the machine. The line and neutral terminals of the coupler will connect to the X and Y terminals of the plug. Because the inlet on the machine is non-polarised, it does not matter that both wires will be hot, instead of hot and neutral.

Larger 240V outlets such as 30A and 50A rated types used for stoves and dryers will supply the necessary power but the breaker will not offer adequate protection to the machine cable. You would need to down-rate the circuit to say 20A or add a local breaker box with a smaller outlet.

Ensure codes are met regarding ground fault protection if required.
I have to agree with @Lucien and good luck with your project
 
OP
J
Reaction score
0
Typical residential supplies in the USA are 120V / 240V split-phase with two hot wires and a neutral. Domestic appliances typically use one hot and neutral for 120V, but stoves, dryers, A/C etc use the two hots to supply 240V and this configuration will power your apple grinder.

You will need a 240V grounded outlet to plug the machine into; it does not matter whether the outlet has a neutral or not, as the machine won't need it, only the two hots and ground. Therefore either of the two common types of 240V receptacle, type 6 (without neutral) or type 14 (with neutral) will suit. Then you would make a cable from a matching plug, (e.g. if you have a 14-20R receptacle then a 14-20P plug) to Schuko inline coupler to fit the machine. The line and neutral terminals of the coupler will connect to the X and Y terminals of the plug. Because the inlet on the machine is non-polarised, it does not matter that both wires will be hot, instead of hot and neutral.

Larger 240V outlets such as 30A and 50A rated types used for stoves and dryers will supply the necessary power but the breaker will not offer adequate protection to the machine cable. You would need to down-rate the circuit to say 20A or add a local breaker box with a smaller outlet.

Ensure codes are met regarding ground fault protection if required.
Thanks so much for taking the time to explain this. A friend recommended I use a step down transformer and a normal 120v outlet, would this be advisable?
 

Lucien Nunes

-
Mentor
Esteemed
Arms
Reaction score
9,965
That is also possible, although it is a step-up transformer you need (120 -> 230V) not step-down. The machine is rated at 1900W but we have to guess the power factor because it does not state the current (The current on the starter label is the starter rating, not the motor.) If we call the pf 0.85 at full load then the load on the transformer will be 1900/0.85=2.2kVA so you would want a transformer with a continuous rating of 2.5kVA or more. If the transformer efficiency is 90% then at full load, based on that guess of power factor, the current on the 120V input side will be just over 20A. In theory this is too high for any normal outlet branch circuit so you would need to put in a 30A 120V circuit to feed the transformer. In practice it is not going to run at full load continuously and we don't actually know the running current. But it's worth drawing that possibility of marginally overloading a 20A 120V outlet to your attention.
 

Marvo

-
Staff member
Mentor
Esteemed
Arms
Supporter
Reaction score
9,843
If it's a 'dumb' or anaolgue machine then as per Lucien it should run on the USA 240v split phase. If it's got internal electronics with any kind of coms it may need a low N-E voltage (<1.5v) in which case it might not work correctly or may even be damaged by a split phase supply. If it's got complex electronics built-in I'd play it safe by using an isolating transformer with one of the output legs referenced to ground.
 
OP
J
Reaction score
0
That is also possible, although it is a step-up transformer you need (120 -> 230V) not step-down. The machine is rated at 1900W but we have to guess the power factor because it does not state the current (The current on the starter label is the starter rating, not the motor.) If we call the pf 0.85 at full load then the load on the transformer will be 1900/0.85=2.2kVA so you would want a transformer with a continuous rating of 2.5kVA or more. If the transformer efficiency is 90% then at full load, based on that guess of power factor, the current on the 120V input side will be just over 20A. In theory this is too high for any normal outlet branch circuit so you would need to put in a 30A 120V circuit to feed the transformer. In practice it is not going to run at full load continuously and we don't actually know the running current. But it's worth drawing that possibility of marginally overloading a 20A 120V outlet to your attention.
Makes sense, thank you again for taking the time to explain everything so thoroughly, I appreciate it! I am unsure that I have a 240v outlet where I will be making the cider so this seems like it might be the only option
 
OP
J
Reaction score
0
That is also possible, although it is a step-up transformer you need (120 -> 230V) not step-down. The machine is rated at 1900W but we have to guess the power factor because it does not state the current (The current on the starter label is the starter rating, not the motor.) If we call the pf 0.85 at full load then the load on the transformer will be 1900/0.85=2.2kVA so you would want a transformer with a continuous rating of 2.5kVA or more. If the transformer efficiency is 90% then at full load, based on that guess of power factor, the current on the 120V input side will be just over 20A. In theory this is too high for any normal outlet branch circuit so you would need to put in a 30A 120V circuit to feed the transformer. In practice it is not going to run at full load continuously and we don't actually know the running current. But it's worth drawing that possibility of marginally overloading a 20A 120V outlet to your attention.
Another question, if going the transformer route what type of plug should I wire to? I have a friend who has offered to let me use this: https://www.amazon.com/Rockstone-5000-Watt-Transformer-Converter/dp/B00J0CF8W4
 

Avo Mk8

-
Esteemed
Reaction score
417
Another question, if going the transformer route what type of plug should I wire to? I have a friend who has offered to let me use this: https://www.amazon.com/Rockstone-5000-Watt-Transformer-Converter/dp/B00J0CF8W4
That converter has a 'universal' output socket ?, which will accomodate a European Schuko male plug, the same format as is fitted to your apple grinder, so that seems an obvious choice.

A US 3-pin plug (as is fitted to the converter) might be a bad idea because someone is bound to plug your grinder in to a 110v socket at some point, and wonder why it doesn't work properly.
 

Lucien Nunes

-
Mentor
Esteemed
Arms
Reaction score
9,965
That converter has a 'universal' output socket ?, which will accomodate a European Schuko male plug,
Well the pins of the plug will fit but it won't make contact with the side earth contacts so not a good choice!. A NEMA 6-15P or 6-20P 240V plug might fit although as per the smiley those sockets don't always make good contact with anything. A UK 13A 240V plug would probably be OK.

Those low- cost transformers are a bit of a con, their rating is lower than the number suggests. E.g. the description for the 5kVA version says it's only suitable for appliances up to 3kVA. That makes it a 3kVA transformer in my book. But it should do your job, 120V input plug overload possibility notwithstanding.
 

Reply to Question about using a 230v appliance here in the USA in the Electrical Forum area at ElectriciansForums.net

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

Search Forum

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top