nazoom

Hi

I am trying g to fill in the Electrical Installation Condition Report, section J. my question is regarding checking the boxes in the section Main protective Conductors. If I have a high value for main protective conductors say to incoming water. What happens to the box Connection / continuity verified for main provide bonding conductor? Do I put X on connection verified or do I put a tick in the connection verified? And then off course I ll put X on the box for incoming to water service.

The installation is TN-S, Domestic.

Many thanks.
 
if the bonding conductors exist and you can confirm this , then you put a tick in the verified box.

if the conductors are damaged , undersized or any other problem , then record this in the defects section , but still tick the box to say they are there.
 
So what happens to the box for incoming water and incoming gas. Do i tick them as well if there was a fault or do i put X?
 
you put x if it doesn't exist, you tick if it's there, you put N/A if t isn't applicable, if it is there then tick and if theres a problem then make a note about it in the area asking about defects etc, simples
 
Agreed, if the connection is there then you tick the box. You may want to make an observation if the reading doesnt make to magical 0.05 ohms once you have considered all the factors that could effect the reading (e.g. length of cable run. x-sectional area etc ... )
 

Reply to Question regarding filling in the box for verification of Main bonding Conductor. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
665
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock