whether your with niceic, napit, elesca etc, please state what questions u can remeber which you had on ur assessment for testing and inspection, include which scheme you was assessed by?......
Discuss Questions asked on your testing assessment in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
1)Did you test the installation. 2)How do you do r1+r2 test,3)how do you test a ring main continuity 3)what should the expected values be 4)how do you perform insulation resistance test 5)what are the minimum values acceptable 6)how do you check polarity/why do you haxe to check polarity 7)how do you test ELI 8)BLAH BLAH RCD each time i explained a test to him he came back with "now you have explained how to do the test can you perform it explaining why results are acceptable" 9)can i pinch one of your smokes, hope thats mature enough for you luke its all i can remember but the guy was ok,give me some good advice. he did ask me one more question now i come to think of it "WHY ARE YOU PUTTING THSE CROCK CLIPS ON MY TESTACLES" SORRY NICEICwhether your with niceic, napit, elesca etc, please state what questions u can remeber which you had on ur assessment for testing and inspection, include which scheme you was assessed by?......
Isn't it because the regs book has the maximum Zs vaule permitted, and the OSG has the "Rule of thumb" values - IE 75% of maximum?
Had me thinking too!
polarity, go to every socket, switch ceiling rose and test line to earth, when energized
R1 + R2 on say a loop in celing rose circuit, link between cpc and line at consumer then go to end of circuit and test there on low ohm scale?
3, What is the max time for a BS EN61008 at x1
No No No
Polarity is prooved as a dead test.
On sockets it's prooved during the Ring cont test
On lighting it's prooved while undertaking the R1+R2 method of continuity.
Yes (make sure you isolate the whole cu)
Watch out for the wording on this question. He could ask what the max time for a BS 61008 at x1 is.
These were asked on my elecsa assesment 08/08/2008
1 How do you tell it's a TNC-S system?
2 What's the max Ze permitted for a TNC-S system?
3 What's the max Ze permitted for a TNS system?
4 Explain how to test a ring circuit and what results you should expect to get?
5 Where are the safe zones?
6 What depth (%) vertically can you chase a wall?
7 what depth (%) horizontally can you chase a wall?
8 What size hole (%) can you drill a floor joist and how far from top and bottam must it be?
9 On a new build what % of the lighting should be low energy?
10 What is the height requirements on a new build for switches and sockets?
Good luck for Friday...............