Discuss Quick IR Test Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
revolt3k
Easy one for ya, when carrying out an IR test on a radiel such as a cooker feed. Do you normally pull the hob and disconnect the cable and then test IR or would connecting Live & Neutral together and testing to earth ok?
Cheers
I would disconnect the cooker from the connection outlet (if one present) and test away. If the lead is just hanging out of the switch then disconnect from there or simply turn it off.
I see what your both saying there guys but the cooker hob is a integral one cut into the work top. So without pulling the oven first and then getting to the hob connections (normally taking the hob out) in unable to disconnect easily. If i turn the switch off and test dont i have to then test the 6mm that feeds the hob?
Many Thanks
you could test through the switch and upto the hoband oven l-e and n-e these should be clear anyway, you may get l-n also if there is no digi clock on the oven try 250v 1st
The oven is on its own 2.5mm radiel that is isolated via a plug top so that one is ok i can just unplug the oven and test away. Would testing the hob circuit harm the hob if i dont disconnect it? Its a touch button with no actual buttons just those that you put your finger on to turn on and off etc.
Just isolate at the cooker isolator and test.
Hobs with touch sensitive buttons will give a false reading, and then probably not work again if you fire 500V at it!
Reply to Quick IR Test Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...