hi guys and girls,
any ideas on why when cunducting an R1 and R2 and also polarity when it was a closed circuit i had 1.87 ohms but when opened circuit 238ohms. this was on a lighting circuit pme system all correctly main bonded and zs complied.
thanks
 
Was the main switch still on at the CU? If there were other lights in the circuit with their switches "on" then the measuring current can run from the CPC through the N-E connection up the neutral through the light bulb and back to your line conductor, then you are measuring the resistance of the light bulbs "on" in the circuit.
 
yes, it was just that circuit i was working on so just that circuit isolated. it was a tidy job before me, they looped the live out the com in a 2gang switch then used the earth as a switch live, then at the ceiling light connected the earth to a single and ran it to the wall light's. all earth's cut off on class 1 fittings. been like it years he said. been put right now.
 

Reply to R1 and R2 parallel earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
787
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
HI everyone I'm getting 255 volts between live and earth natural to live on a live lighting circuit fed from 6amp rcbo , When switch off I'm...
Replies
1
Views
846

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock